#86812 - 12/14/03 12:07 PM Subpanel with out a main?
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Can i install a double pole 100Amp breaker into a 125Amp main lug 24circuit panel and call it the main disconnect for that subpanel?
Please give NEC sections.


edward
_________________________
Thanks
Edward
Top
2017 / 2014 NEC & Related Books and Study Guides
#86813 - 12/14/03 02:14 PM Re: Subpanel with out a main?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
408.16(F) permits this type of installation.
Top
#86814 - 12/14/03 02:52 PM Re: Subpanel with out a main?
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
You need to make sure the loadcenter is listed for using a back-fed main breaker and if so they often will only permit it in a specific location which is designed to accept the required hold down kit. This information should be on the label. Many newer loadcenters are designed to accept main breaker kits that mount in place of the main lugs.

Curt
_________________________
Curt Swartz
Top
#86815 - 12/14/03 05:35 PM Re: Subpanel with out a main?
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Thanks for the reply.
Can i back feed the busbars with a 100Amp breaker and call that the main? Or it has to be a kit that goes in the place of the main lugs?

Edward
_________________________
Thanks
Edward
Top
#86816 - 12/14/03 09:18 PM Re: Subpanel with out a main?
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Yes, you can back feed a breaker in the loadcenter if the instructions on the loadcenter say you can. You are required to secure the back fed breaker so you must purchase a hold down kit that fits the breaker and loadcenter. The hold down kits often will only fit in the one designated position in the loadcenter. If there are provisions to replace the main lugs with a main breaker that is usually the better way to go. Many Square D and GE loadcenters have main breaker kits to replace the main lugs.

Curt
_________________________
Curt Swartz
Top
#86817 - 12/15/03 08:41 AM Re: Subpanel with out a main?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals