The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (HotLine1), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#86784 - 12/09/03 12:01 PM Grounding/bonding residential services
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
I need some help with 2002 NEC references to clarify an issue. Here's the situation:
My local REMC is the last electric utility in the area that still wants a grounding electrode connection from their meter base to the grounding electrode. All other utilities in the area forbid this and want to see this connection made only in the first means of OCP. This REMC had the same line super and operations manager for the last 42 years and it was policy to require the connection in the meter base, grounding the neutral there and nowhere else. Well now they have a new Ops manager and a new line super. The line super is a 27 year lineman and a good common sense guy. The Ops manager is also a good guy but he is now requiring an additional GEC to be ran from the grounding electrode to the main OCP. The line super doesn't think this is right and contacted me for specific code references to support his position since he isn't and hasn't had to be well versed in the NEC in his career as a lineman/serviceman with the utility. His take on the situation is that the neutral should be grounded at the first means of OCP and no GEC connection should be made in the meter base. The meterbase is bonded to the neutral and with the neutral being bonded in the main OCP that bonds the meter base enclosure. My understanding is the service neutral should only be bonded in one place, either the meterbase or the main OCP, to avoid parrallel(sp) paths. The line super is asking for my help so he can pitch a policy change to the board next month with sound references for his proposal. He would like to see this REMC get on the same page as the surrounding utilities. He is to be commended, in my opinion. Specific 2002 code article references would be much appreciated. Thanks in advance.

Top
2014 / 2011 NEC & Related Books and Study Guides
#86785 - 12/09/03 03:37 PM Re: Grounding/bonding residential services
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Fred,

Can you get some input from the neighboring Utilities? It seems it would be in their best interest to be on the same page too.

Bill

Top
#86786 - 12/09/03 05:40 PM Re: Grounding/bonding residential services
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
Bill,
The neighboring utilities policy is no ground connection in a sealed meter base. They don't want anyone other than the utility to have a reason to be in there. One utility sites parallel ground path but doesn't back it up with any code substantiation.

Top
#86787 - 12/09/03 06:04 PM Re: Grounding/bonding residential services
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Fred,

There is a picture in the NEC handbook on page 182 which shows that the grounding electrode conductor (GEC.) The figure (Exhibit 250.8)shows that the GEC can be connected at the service head, service meter enclosure or in the service equipment. That is as per sec. 250.24(A)(1) However some utilities don't want the GEC attached in their meter enclosure, if you look at 250.68(A) the GEC shall be accessible. Maybe once the meter is locked off, the GEC is no longer accessible.

Top
#86788 - 12/09/03 06:52 PM Re: Grounding/bonding residential services
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
I'm with you Harold. My question is, Can or should you require the neutral to be grounded in the meter base AND in the disconnect? I'm thinking one or the other but not both. If it doesn't matter if we bond at both places why don't we bond at every sub panel down-stream from the main?
I think I know why but I need code references to back it up. Thanks for your input.

Top
#86789 - 12/09/03 07:04 PM Re: Grounding/bonding residential services
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
I wouldn't consider inside the meter unaccessable.

If the GEC connection was a problem connection, wouldn't the current carrying conductors be more so?

Although it might be agravating, we can get access back into a meter enclosure.

Harold 250.68(A) would be the connection to the electrode.

Fred, I would point out 250.6(A), you might need to draw out the scenario of multiple paths to accompany this code reference.

Good luck

Roger

Top
#86790 - 12/09/03 07:14 PM Re: Grounding/bonding residential services
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Our utility requires the GEC from the ground rod be connected in the meter can. The GEC from the water pipe or other electrodes is connected at the service disconnect. 250.24(A)(1) permits the GEC connection to be made at any point on the line side of the service disconnect. I do not find any rule in the NEC that requires all of the grounding electrodes to use a common grounding electrode conductor nor a rule that says multiple grounding electrode conductors must be connected to the grounded conductor at a common point.
Don
_________________________
Don(resqcapt19)

Top
#86791 - 12/09/03 07:29 PM Re: Grounding/bonding residential services
txsparky Offline
Member

Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
Our PoCo (Entergy) actually requires parallel paths.
This is from their installation standards...
 Quote:
11.10 Meter Grounding
Grounding the metering installation is a safety consideration both for the
Company and the Customer. The grounding connection shall be made in
accordance with NEC Article 250 and any other referenced code and preferably
in the meter socket. If the grounding connection is made anywhere other than
the meter socket, the Customer shall be responsible for grounding continuity
between the point where the grounding is made and the meter socket.


[This message has been edited by txsparky (edited 12-09-2003).]
_________________________
Donnie

Top
#86792 - 12/09/03 08:12 PM Re: Grounding/bonding residential services
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
txsparky,

Are you saying that Entergy requires that neutral be bonded to the meter socket ground even if the neutral is bonded to the ground elsewhere?

I would read the paragraph that you quote as requiring that the meter socket be grounded, but _not_ requiring that the neutral be bonded to ground in the meter socket. If the bond between neutral and ground is elsewhere (eg in the main disconnect), then the customer is responsible for proper ground continuity to between the meter socket and the point of the ground bond.

I don't see a required parallel path unless it is required to bond ground to neutral in the meter socket.

-Jon

Top
#86793 - 12/09/03 08:23 PM Re: Grounding/bonding residential services
txsparky Offline
Member

Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
Winnie,
The neutral lug(s) in the meter can are bonded to the can. They are not mounted on insulators.
_________________________
Donnie

Top