The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (jraef, LongRunner), 188 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86772 - 12/03/03 04:15 PM GEC can be Green or Green with a Yellow Stripe!
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Report on Comments - May 2004
196 Log #385 NEC-P05
(250. 119)
Submitter: Dan Leaf Rancho Santa Margarita, CA
Comment on Proposal Number: 220
Recommendation:

Revise last sentence: Conductors with insulation or individual covering that is green , green with one or more yellow stripes , or otherwise identified as permitted by this section shall be used only as an equipment bonding conductor.

Exception: Grounding electrode conductors shall be permitted to be identified in accordance with this section.

Substantiation:

Since this section encompasses individual covered conductors, they should be covered by the proposal. Many installers employ green covering, marking, or striping for grounding electrode conductors , though not required or prohibited by present Code, which provides a degree of identification from circuit conductors, especially where installed with other conductors in the same raceway or enclosure. Though this section relates to equipment grounding (bonding) conductors the wording appears applicable as a general rule.

Final Action:

CMP 5 Accepted this "Comment in Principle" and added the following to the existing 250.119 in the NEC.

"Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for grounded or ungrounded circuit conductors"



[This message has been edited by Joe Tedesco (edited 12-04-2003).]
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#86773 - 12/04/03 03:11 PM Re: GEC can be Green or Green with a Yellow Stripe!
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
the sqeaky wheel method seems very effective in the nfpa...

Top
#86774 - 12/14/03 02:29 AM Re: GEC can be Green or Green with a Yellow Stripe!
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
While specifying that green (or green/yellow) be used for grounding conductors, it seems only logical to me that these colors should also be prohibited from use for other functions.

Top
#86775 - 12/14/03 08:34 AM Re: GEC can be Green or Green with a Yellow Stripe!
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
 Quote:
"Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for grounded or ungrounded circuit conductors"
It only makes sense to close a loophole when one is found.


Bill

Top