#86772 - 12/03/03 04:15 PM GEC can be Green or Green with a Yellow Stripe!
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Report on Comments - May 2004
196 Log #385 NEC-P05
(250. 119)
Submitter: Dan Leaf Rancho Santa Margarita, CA
Comment on Proposal Number: 220
Recommendation:

Revise last sentence: Conductors with insulation or individual covering that is green , green with one or more yellow stripes , or otherwise identified as permitted by this section shall be used only as an equipment bonding conductor.

Exception: Grounding electrode conductors shall be permitted to be identified in accordance with this section.

Substantiation:

Since this section encompasses individual covered conductors, they should be covered by the proposal. Many installers employ green covering, marking, or striping for grounding electrode conductors , though not required or prohibited by present Code, which provides a degree of identification from circuit conductors, especially where installed with other conductors in the same raceway or enclosure. Though this section relates to equipment grounding (bonding) conductors the wording appears applicable as a general rule.

Final Action:

CMP 5 Accepted this "Comment in Principle" and added the following to the existing 250.119 in the NEC.

"Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for grounded or ungrounded circuit conductors"



[This message has been edited by Joe Tedesco (edited 12-04-2003).]
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#86773 - 12/04/03 03:11 PM Re: GEC can be Green or Green with a Yellow Stripe!
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
the sqeaky wheel method seems very effective in the nfpa...
Top
#86774 - 12/14/03 02:29 AM Re: GEC can be Green or Green with a Yellow Stripe!
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
While specifying that green (or green/yellow) be used for grounding conductors, it seems only logical to me that these colors should also be prohibited from use for other functions.
Top
#86775 - 12/14/03 08:34 AM Re: GEC can be Green or Green with a Yellow Stripe!
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Quote:
"Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for grounded or ungrounded circuit conductors"
It only makes sense to close a loophole when one is found.


Bill
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 46 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals