#86754 - 12/02/03 05:57 PM arc welder OCP
Tim Peters Offline
Member
Registered: 03/08/03
Posts: 10
I'm installing a dedicated circuit for a portable arc welder. The min. rating is 15 amps at 120 volts and the max is 20 amps at 120 volts. Article 630-12 state that the OCP shall not be more than 200% of the max. My question is, what would be optimal? Should I install a 20 amp OCPD based off the MAX on the nameplate of the welder or should I use the Maximum stated by the NEC?

This kind of confused me because the code states no minimum only a maximum.
Top
2017 / 2014 NEC & Related Books and Study Guides
#86755 - 12/03/03 01:28 PM Re: arc welder OCP
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
I believe that if the nameplate specified a 20A max OCPD, thats what I would use.
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 109 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals