The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86754 - 12/02/03 05:57 PM arc welder OCP
Tim Peters Offline
Member

Registered: 03/08/03
Posts: 10
I'm installing a dedicated circuit for a portable arc welder. The min. rating is 15 amps at 120 volts and the max is 20 amps at 120 volts. Article 630-12 state that the OCP shall not be more than 200% of the max. My question is, what would be optimal? Should I install a 20 amp OCPD based off the MAX on the nameplate of the welder or should I use the Maximum stated by the NEC?

This kind of confused me because the code states no minimum only a maximum.

Top
2014 / 2011 NEC & Related Books and Study Guides
#86755 - 12/03/03 01:28 PM Re: arc welder OCP
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
I believe that if the nameplate specified a 20A max OCPD, thats what I would use.