The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86745 - 11/26/03 08:13 PM Assembly in a Raceway
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
Can someone cite for me the article for the rule that an assembly cannot be installed in a raceway.

I know it's in there but cannot remember where to find it.
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top
2014 / 2011 NEC & Related Books and Study Guides
#86746 - 11/27/03 01:48 AM Re: Assembly in a Raceway
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Pete are you talking about cables?

Right now in the 2002 code cycle only type MC is specifically allowed in a raceway. 330.10(7)

For 2002 part of section .22 of the raceway articles was changed to this wording.

 Quote:
XXX.22 Cables shall be permitted to be installed where such use is permitted by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.


Right now type MC is the only one I know that says it is permitted in raceways.

Previously NM, UF, SE and MC could all be in raceways.

I have heard in the 2005 code you will again be able to put these cables in raceway.

I have been told it was a case of one hand not knowing what the other was doing.

All this does not change the fact that you can and are sometimes required to put any of these cables in a "short section" of raceway for physical protection.

Another forum member asked the NFPA for an official interpretation of "short section" and the reply was less than a full length of raceway.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#86747 - 11/27/03 06:23 AM Re: Assembly in a Raceway
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
I looked and looked and I did previously find the XXX.22 you refrenced. Yet I could not find any refrence to conduit fill, etc. which allows it.
I may have misstated my question. I was basically referring to conduits. I know about the physical damage rule for short sections.
I was always under the impression that NM, etc. could not be used in a raceway or conduit. In fact I had been told by an inspector more than once. Once we had to temporarily run a piece of romex in a short conduit and was told make sure we change it, which of course we did.
There is something about the temp rating of the conductors and an assembly in a conduit would create an unintended rise in temperature due to the added insulation.

I see this is more of a contentious issue than I thought.
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top
#86748 - 11/27/03 06:33 AM Re: Assembly in a Raceway
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Try this link for some more info.

http://www.electricalmatters.com/forum/viewtopic.php?t=138

The raceway will create no more heat build up for a cable then for the same number of single carrying conductors.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts