#86716 - 11/24/03 01:50 PM 100A sub redux
buckyswider Offline
Junior Member
Registered: 11/24/03
Posts: 2
Loc: Cold Point, PA, USA
Wow, spent the afternoon searching the archives re 100A subpanel. Bazillions of posts, opinions, and interpretations, but no consensus, but the safe way(s) to go are either:

1) Install 90A cb on feeder panel for #4 CU;
or
2) Use #3 CU.

(BTW, I plan on THHN).

Question about option #2- the neutral & grounding bars on the main panel are only rated for up to a #4 CU. What do I do with my grounded & grounding wires if I use #3?

Yes, I've removed the bonding jumper from my sub. Will make sure that neutral bars get only grounded conductors, and grounding bars get only grounding counductors.

Thanks!
Top
2017 / 2014 NEC & Related Books and Study Guides
#86717 - 11/24/03 02:41 PM Re: 100A sub redux
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Check the manufacturers catalog. Sometimes they make an auxilliary lug that will fasten into a couple of the neutral bus holes. I know that GE and Square D make these for their panels.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals