#86560 - 11/10/03 01:44 PM groud connection
gserve Offline
Member
Registered: 03/11/03
Posts: 92
I have a 100A disconnect on a pole that is going to feed a mobile home.The problem is that the neutral bar doesn
't have room to accommodate both the neutral and the ground connection. Question; Can I attach a bolt-on lug by machine screw to the enclosure to pick up the ground wire. This is the main service and the enclosure is bonded to the neutral bar.
Top
2017 / 2014 NEC & Related Books and Study Guides
#86561 - 11/11/03 02:53 AM Re: groud connection
zapped208 Offline
Member
Registered: 02/18/03
Posts: 196
Loc: Somewhere in USA
Will your POCO let you ground it in the meter base? If they do, your AHJ should pass your inspection. My inspectors would accept the bolt and nut thing, but I know it will take a bashing here.
_________________________
Shoot first, apologize later.....maybe
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals