The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 237 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86557 - 11/10/03 01:41 PM Service sizing
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I was asked by a local electrical contractor to stop by their shop and help train the electricians on service/grounding/bonding sizing.

Please take a minute and review this drawing I created. PLEASE let me know if you find any errors in it. Thank you.



[This message has been edited by Ryan_J (edited 11-10-2003).]
_________________________
Ryan Jackson,
Salt Lake City

Top
2014 / 2011 NEC & Related Books and Study Guides
#86558 - 11/10/03 02:31 PM Re: Service sizing
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Ryan,
You don't have enough 600 kcmil cables for a 1600 service. You need 4 sets, which changes the line side bonding jumper to 300 kcmil.
Don
_________________________
Don(resqcapt19)

Top
#86559 - 11/10/03 02:33 PM Re: Service sizing
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
EEK!!!!!

Thats why I posted this! I used the same diagram here that I used for a 1200A!!!

I had this for a 1600A, then I deleted (1) pipe on the feeder and one on the service entrance conductors, but I overlooked changing the rating of the fuses! (embarrassed)

thanks Don!

[This message has been edited by Ryan_J (edited 11-10-2003).]
_________________________
Ryan Jackson,
Salt Lake City

Top