The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 226 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86345 - 10/15/03 01:05 PM Phase conductors through same hole
Mike Wescoatt Offline
Member

Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah
I'm having a tough time finding it today...
Where is the Code reference for having all current carrying conductors enter an enclosure through the same hole, single holes with slots, or single holes through a non-magnetic plate?
Thanks!!!
_________________________
Mike Wescoatt

Top
2014 / 2011 NEC & Related Books and Study Guides
#86346 - 10/15/03 01:24 PM Re: Phase conductors through same hole
Creighton Offline
Member

Registered: 01/06/02
Posts: 56
Loc: Hayward, CA
Try 300.20 Creighton