The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 201 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86334 - 10/14/03 06:57 AM Ground Fault Protection
rusty1 Offline
Junior Member

Registered: 10/13/03
Posts: 2
Loc: Mt Union, PA USA
Need a little help in confirming my interpretation of 427 and specifically 427.22 from 2002 code. It appears that only electric heating systems that utilize heat trace or flexible heating panels require ground fault protection? Is this because they have no grounded external sheath as in earlier editions of the code?

Top
2014 / 2011 NEC & Related Books and Study Guides
#86335 - 10/14/03 08:32 AM Re: Ground Fault Protection
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Rusty,
The heat tape and heating panels must have a grounded conductive coating. Note that in previous codes, this covering was required to be metallic, but in the 2002 code it was changed to permit nonmetallic conductive coatins to be used. See 427.23. GFP was required even when the heat trace had a grounded metallic covering. The GFP is required because resistance heating can fail in a manner that will produce enough heat to start a fire without pulling enough current to open the overcurrent protective device.
Don
_________________________
Don(resqcapt19)

Top
#86336 - 10/14/03 09:07 AM Re: Ground Fault Protection
rusty1 Offline
Junior Member

Registered: 10/13/03
Posts: 2
Loc: Mt Union, PA USA
Thanks a lot Don,
I guess I just wondered what makes the heat tape different say from a hot water heater or the numerous other resistance heater apps that do not require GF protection.

Top
#86337 - 10/14/03 10:39 AM Re: Ground Fault Protection
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Rusty,
I think that there is a lot more potential for damage to heat tracing than other types of resistance heating.
Don
_________________________
Don(resqcapt19)

Top
#86338 - 10/17/03 04:15 AM Re: Ground Fault Protection
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I'll second Don on the damage issue.
When installed under pipe insulation, in order to help minimize potential damage, the outer sheath of the insulation should even have warning stickers(supplied from the manufacturer)to indicate that electric heat tracing is installed underneath.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals