#86331 - 10/08/03 03:39 PM Mobile home grounding
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
I'm looking at the current requirements for the service connection to a mobile home.

Per the 2002 NEC, 550.16, and part (A)(1) specifically, clearly requires that neutral and ground must be kept separate on the mobile home and prohibits the grounding of appliance frames to the neutral. 550.10(B) specifies a 4-wire supply cord.

550.16(C)(1) requires that the chassis be bonded to the grounding bus in the panel.

Question:
I was browsing another site and read an item which suggests that in the past it was allowable for a mobile home to be fed via a 3-wire connection with N-Gnd bond at the panel.

Is this true?

How about the requirement of 550.16(C)(1) to bond the chassis -- Has this always been the case?

P.S. I'm ignoring the exception which allows N-Gnd bonds if the service equipment is attached to a "manufactured home" in accordance with 550.32(B), and just assuming that the service is located on a nearby post.


[This message has been edited by pauluk (edited 10-08-2003).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#86332 - 10/08/03 06:02 PM Re: Mobile home grounding
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
I don't think the N-Gnd bond at the panel has been allowed at keast since the early 1970s.
Top
#86333 - 10/11/03 03:02 PM Re: Mobile home grounding
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
So 30+ years of 4-wire supplies? Thanks.

Grounding and bonding issues seem to be an area where ideology changes over the years, both in the U.S.A. and the U.K.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals