#86063 - 09/04/03 06:58 PM CB and enclosure mismatch, violation?
KenO Offline
Junior Member
Registered: 02/03/03
Posts: 3
Loc: Prior Lake, Mn USA
Can anyone enlighten me in what article it address's the violation of using a different manufactueur' breaker in someone elses pnl/loadcenter.

Ie... using a ITE breaker in a Crouse hinds load center

Thanks

Ken
Top
2017 / 2014 NEC & Related Books and Study Guides
#86064 - 09/04/03 07:02 PM Re: CB and enclosure mismatch, violation?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
110.3(B). (the hardest article in the world to enforce!) I have e-maile a couple different manufacturers and they have replied that their products are not listed for use with other panels/breakers. I do believe that are a very few breakers that are listed for use in other panels, but are the panels listed to recieve them? I doubt it.
_________________________
Ryan Jackson,
Salt Lake City
Top
#86065 - 09/04/03 11:16 PM Re: CB and enclosure mismatch, violation?
NORCAL Offline
Member
Registered: 09/25/02
Posts: 865
I-T-E is owned by Seimens and they bought the Crouse-Hinds/Murrey line, you should be able to get a letter from them on approved
replacements.
Top
#86066 - 09/05/03 09:00 AM Re: CB and enclosure mismatch, violation?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
While the panel manufacturers will tell you that you can only use thier listed breakers in the panel, that is not correct and is one of the reasons that 110.3(B) only applies to instructions that are part of the listing and labeling. 110.3(B) does not require compliance with manufacturers instructions. There are UL "classified" breakers that are permitted to be used in panels made by other companies. The use of these "classified" breakers is code compliant and does not void the panel listing.
See UL Guide DIXF. "This category(DIXF) covers Classified molded-case circuit breakers rated 15 to 50 A, 120/240 V maximum that have been investigated and found suitable for use in place of other Listed circuit breakers in specific Listed panelboards." Note that classified breakers are required to be supplied with a list of panels that they can be used in.
Don



[This message has been edited by resqcapt19 (edited 09-05-2003).]
_________________________
Don(resqcapt19)
Top
#86067 - 09/08/03 06:06 PM Re: CB and enclosure mismatch, violation?
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
Does a manufacturer have to honor a warranty if you don't follow their instructions as long as the product is used as listed?

I know this issue is not enforceable, but it is something additional to think about. Then again I've never seen anyone return a panel because of a manufacturer defect.
Top
#86068 - 09/08/03 06:43 PM Re: CB and enclosure mismatch, violation?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Steve,
I did some reserch on the warranty issue a few months ago. It appears that if a contractor installs the "classified" breaker that the panel manufacturer could void the warranty, but if the building owner or end user installs the classified breaker, the warranty stands.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals