The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
2 registered (Tjia1981, sparkyinak), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#86017 - 08/30/03 04:49 PM Additional bathroom receptacles.
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Is an additional receptacle in a bathroom, for a towel bar/heater, permitted to be fed from the general lighting circuit that supplies the bathroom, or would it have to be fed from the 20-amp bathroom circuit?

2014 / 2011 NEC & Related Books and Study Guides
#86018 - 08/30/03 06:52 PM Re: Additional bathroom receptacles.
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
This is an interesting question, here is how I see it.
If the bathroom has a dedicated 20 amp circuit, it can be taken from the 20 amp circuit. IF the lighting is not from that circuit, no it cannot be taken from the lighting circuit.
Provided the towel bar is not hardwired, and is cord and plug connected, the receptacle will also be required to be GFCI protected.

Pierre Belarge

#86019 - 08/31/03 05:31 AM Re: Additional bathroom receptacles.
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thanks for the input, Pierre.
They also now want a receptacle for TV.
Same questions arise, and I'm inclined to agree with you.

#86020 - 08/31/03 06:19 PM Re: Additional bathroom receptacles.
Jim M Offline

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA

Why would the additional receptacle need to be on the receptacle circuit instead of the lighting if the lighting circuit were separate? I would agree on the need for GFI protection but can't see adding additional loads when blow dryers are now up to 1875 watts.

your thoughts?

#86021 - 08/31/03 06:46 PM Re: Additional bathroom receptacles.
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
I agree with what was said, Pierre and Redsy. I read 210.11(C)(3) to require all bathroom receptacle outlets on the 20A bathroom circuit unless you use the exception to put all loads of one bathroom on that one circuit.
And 210.8(A)(1) just says bathrooms, so all recepts in the bathroom must be GFCI.

You could always add another 20A recept circuit to the bathrooms (permitted by 210.11(C)(3)) for the TV and towel bar warming unit, but it sounds like you want to tap close by.

[This message has been edited by Ron (edited 08-31-2003).]