#86017 - 08/30/03 04:49 PM Additional bathroom receptacles.
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Is an additional receptacle in a bathroom, for a towel bar/heater, permitted to be fed from the general lighting circuit that supplies the bathroom, or would it have to be fed from the 20-amp bathroom circuit?
Top
2017 / 2014 NEC & Related Books and Study Guides
#86018 - 08/30/03 06:52 PM Re: Additional bathroom receptacles.
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
Redsy
This is an interesting question, here is how I see it.
If the bathroom has a dedicated 20 amp circuit, it can be taken from the 20 amp circuit. IF the lighting is not from that circuit, no it cannot be taken from the lighting circuit.
Provided the towel bar is not hardwired, and is cord and plug connected, the receptacle will also be required to be GFCI protected.

Pierre
_________________________
Pierre Belarge
Top
#86019 - 08/31/03 05:31 AM Re: Additional bathroom receptacles.
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks for the input, Pierre.
They also now want a receptacle for TV.
Same questions arise, and I'm inclined to agree with you.
Top
#86020 - 08/31/03 06:19 PM Re: Additional bathroom receptacles.
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
PC,

Why would the additional receptacle need to be on the receptacle circuit instead of the lighting if the lighting circuit were separate? I would agree on the need for GFI protection but can't see adding additional loads when blow dryers are now up to 1875 watts.

your thoughts?
Top
#86021 - 08/31/03 06:46 PM Re: Additional bathroom receptacles.
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
I agree with what was said, Pierre and Redsy. I read 210.11(C)(3) to require all bathroom receptacle outlets on the 20A bathroom circuit unless you use the exception to put all loads of one bathroom on that one circuit.
And 210.8(A)(1) just says bathrooms, so all recepts in the bathroom must be GFCI.

You could always add another 20A recept circuit to the bathrooms (permitted by 210.11(C)(3)) for the TV and towel bar warming unit, but it sounds like you want to tap close by.

[This message has been edited by Ron (edited 08-31-2003).]
_________________________
Ron
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals