The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
1 registered (annemarie1), 302 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85979 - 08/24/03 01:19 PM Load Diversity
Surge Offline
Junior Member

Registered: 05/31/03
Posts: 2
Loc: Jacksonville, FL, USA
In reference to Table B310-11, what exactly does a 50% load diversity mean?

2014 / 2011 NEC & Related Books and Study Guides
#85980 - 08/24/03 07:49 PM Re: Load Diversity
WebSparky Offline

Registered: 02/21/03
Posts: 144
Loc: Cleveland, Ohio
The factors in the second column of Table 310.15(B)(2)(a) are based on no diversity, meaning that all conductors in the raceway or cable are loaded to their maximum rated load. For load diversity, the user is directed to Annex B.

#85981 - 08/26/03 07:01 PM Re: Load Diversity
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA

I always took it to mean that the average loading of all the wires in the conduit was at about half the total calculated load.
However, now I'm wondering if my reasoning is circular. Maybe it's one of those things that you think you understand, but can't explain it.

For example,

If 12 #6 THWN copper conductors (basic ampacity, 65 amps per Table 310.16) are installed in a single conduit, Table 310.15(B)(2)(a) requires a reduction to 50%, or 32.5 amps.
If it can be shown that, at any given time, either half of the conductors would be carrying no current while the others are fully loaded, (or another combination of percentages that would equal the same total current) you are permitted to alter your adjustment factor up from 50% to 70%, for an increase from 32.5 to 45.5 amps.