The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85979 - 08/24/03 01:19 PM Load Diversity
Surge Offline
Junior Member

Registered: 05/31/03
Posts: 2
Loc: Jacksonville, FL, USA
In reference to Table B310-11, what exactly does a 50% load diversity mean?

Top
2014 / 2011 NEC & Related Books and Study Guides
#85980 - 08/24/03 07:49 PM Re: Load Diversity
WebSparky Offline
Member

Registered: 02/21/03
Posts: 144
Loc: Cleveland, Ohio
The factors in the second column of Table 310.15(B)(2)(a) are based on no diversity, meaning that all conductors in the raceway or cable are loaded to their maximum rated load. For load diversity, the user is directed to Annex B.
_________________________
Dave

Top
#85981 - 08/26/03 07:01 PM Re: Load Diversity
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
IMHO,

I always took it to mean that the average loading of all the wires in the conduit was at about half the total calculated load.
However, now I'm wondering if my reasoning is circular. Maybe it's one of those things that you think you understand, but can't explain it.

For example,

If 12 #6 THWN copper conductors (basic ampacity, 65 amps per Table 310.16) are installed in a single conduit, Table 310.15(B)(2)(a) requires a reduction to 50%, or 32.5 amps.
If it can be shown that, at any given time, either half of the conductors would be carrying no current while the others are fully loaded, (or another combination of percentages that would equal the same total current) you are permitted to alter your adjustment factor up from 50% to 70%, for an increase from 32.5 to 45.5 amps.