#85959 - 08/22/03 06:50 AM Bathroom receptacles
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Let me start by saying that I try to leave interperation out of the code, but as we all know, that is not always possible. That being said, I had an electrician ask me about the required receptacle outlet in a dwelling unit bathroom. He has a pedastal sink and wanted to know if the elevation of the required receptacle outlet can be below the basin, as long as it is on the adjacent wall. The NEC doesn't address this. I would like to have some thoughts as to whether or not this meets the "intent" of the code. Thanks in advance for your replies.
_________________________
Ryan Jackson,
Salt Lake City
Top
2017 / 2014 NEC & Related Books and Study Guides
#85960 - 08/22/03 09:52 AM Re: Bathroom receptacles
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
Yes - the receptacle is permitted to below the basin (or counter top).

I quote Jeff Sergeant from NFPA.

At a recent update training class provided by NFPA to building inspectors he (Jeff) specifically addressed this item and assured attendees that a receptacle could be placed below the basin/counter level as long as the receptacle was within 36" of the basin.
Top
#85961 - 08/22/03 10:08 AM Re: Bathroom receptacles
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Dana, As always, thanks for your reply. I told him that I would allow it, my basis was that the NEC didn't strictly prohibit it. Thanks again.
_________________________
Ryan Jackson,
Salt Lake City
Top
#85962 - 08/22/03 11:03 AM Re: Bathroom receptacles
GTE Offline
Member
Registered: 03/26/03
Posts: 48
Loc: Bridgehampton, N.Y. USA
The inspectors in my area will approve basin receptacles if they aren't lower then 12" from the top of basin. The same a kitchen counter outlets.
Top
#85963 - 08/22/03 12:36 PM Re: Bathroom receptacles
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
We had a similar query over this point a while ago:
http://electrical-contractor.net/ubb/Forum2/HTML/000621.html

Does anyone know if Virgil's proposal was ever submitted? If so, what was the outcome?
Top
#85964 - 08/22/03 01:43 PM Re: Bathroom receptacles
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
The current proposed 2005 NEC change shows some relief:

Panel Meeting Action: Accept in Principle

In the 2002 NEC, delete the word "wall" in the first sentence so that it reads:

"In dwelling units, at least one receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin."

Also add an exception to 210.52(D) to read:

"Exception: The receptacle shall not be required to be mounted in the wall or partition where it is installed on the face of the basin cabinet not more than 300 m (12 in.) below the countertop."
_________________________
Joe Tedesco, NEC Consultant
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals