#85867 - 08/12/03 08:31 AM Spa Disconnect
mvrandazzo Offline
Member
Registered: 05/13/02
Posts: 105
This year I have been putting in quite a few spas. I have been locating the disconnect on the outside of the house wall and using Flex non-metalic conduit to pemanently connect the spa. For the most part I had no problems with inspections. Receintly an inspector failled an install stating that the disconnect was located too close to the spa. He said it was to be located not less than 5 feet from the spa. I understood this to apply to cord and plug assemblies only in accordance to Art. 680, ch I and II. 680:12 states that it is to be "readily accessable and within sight of". Am I missing something?

Blessings, Mark
Top
2017 / 2014 NEC & Related Books and Study Guides
#85868 - 08/12/03 08:44 AM Re: Spa Disconnect
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
680.41 requires minimum of 5 ft. distance.
However, it doesn't apply to single-family dwellings. Nonetheless, I see the 5' requirement met regularly.
Top
#85869 - 08/12/03 07:25 PM Re: Spa Disconnect
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Mark,

680.22(C) (Switching Devices) would apply here I think.

Bill
Top
#85870 - 08/12/03 09:14 PM Re: Spa Disconnect
Jim M Offline
Member
Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
Redsy,

Are you sure the 5' doesn't apply in a residential setting? I only thought the emergency stop didn't. Me book is in the truck and I'm ready to hit the sack.
Top
#85871 - 08/13/03 04:03 AM Re: Spa Disconnect
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Jim,
I thought so too, but it isn't stated in 680.12 (although the Handbooks caption under exhibit 680.2 does say so it needs to be minimum 5').
Maybe 680.22 (C)?
Top
#85872 - 08/13/03 06:12 AM Re: Spa Disconnect
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Redsy,

It seems like another poorly worded section, but I believe 680.41 is saying that the Emergency Switch is not required at a single-family residence. It's not saying that the required 5 foot minimum distance is waived.

Bill
Top
#85873 - 08/13/03 07:18 AM Re: Spa Disconnect
mvrandazzo Offline
Member
Registered: 05/13/02
Posts: 105
Thanks for your replies. All this time I assumed it was more clear but now I'm not sure. Bill, I thought 680-22 was refurring to lighting, recepticles and other equipment. It is not hard to be sure I install the disconnect at least 5' from the spa but now that brings up another question. 680-42 permits the use of flexible connections not to exceed 6'. That only leaves 1' left to connect to the spa. The only thing left to do is to connect using shed 40 and convert to flex once inside the spa surround. Either way it is not that big an issue to change the location of the disconnect. I will discuss this with the inspector anyway. Thanks for your thoughts.

Blessings, Mark
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 102 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/19/00
Posts: 2724

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals