The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Parking lot pole light swap....
by HotLine1
Today at 09:39 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 244 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85728 - 07/31/03 02:43 PM Required additional disconnecting means?
EnergyPlus Offline
Junior Member

Registered: 07/31/03
Posts: 1
Loc: Troy, IL, USA
This is a rather unique situation so please let me set this up correctly.

This is for a Streetscape project where decorative streetlights run down both sides of the street. The lighting circuit is unmetered by the utility and I don't think it is in question. There are 4 duplex recepticals at the base of each light and each half is protected by a GFI Breaker.

The meter and panel structure were installed mid block near the sidewalk(above ground). Property owner changed heart and refused to give easement. Meter was moved 100 feet back from sidewalk to alley and underground feeder ran from meter point to end of block to main street and back to center of block near sidewalk (original location). Electrical panels were mounted in a concrete vault under the sidewalk and is accessible by manhole cover. Electrical panels have 20 - 20 amp circuit breakers and a 300 amp main disconnect. Is an additional disconnect required at the meter?

Who would ever know what it controlled and why would it be necessary? These recepticals are only going to be energized 1 or 2 weekends for festivals. Other times the service will be OFF.


2014 / 2011 NEC & Related Books and Study Guides
#85729 - 08/01/03 03:23 AM Re: Required additional disconnecting means?
zapped208 Offline

Registered: 02/18/03
Posts: 201
Loc: Somewhere in USA
No disconnect needs to be added. The conductors that go underground to the vault and panel are still service entance conductors, from the meter.
Shoot first, apologize later.....maybe