#85717 - 07/31/03 11:43 AM Paddle Fan Motor Disconnect ?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Can a paddle (ceiling) fan with a light kit be installed such that a single wall switch operates the light, but the motor is connected directly to the feed ?
Why, or why not?


2017 / 2014 NEC & Related Books and Study Guides

#85718 - 07/31/03 12:37 PM Re: Paddle Fan Motor Disconnect ?  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Yes it can. Why not?


#85719 - 07/31/03 01:36 PM Re: Paddle Fan Motor Disconnect ?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Motor disconnecting means?
Appliance disconnecting means?
What is a typical HP rating of a ceiling fan?

I've wondered about this on occasion.

[This message has been edited by Redsy (edited 07-31-2003).]


#85720 - 07/31/03 07:52 PM Re: Paddle Fan Motor Disconnect ?  
ccdave  Offline
Member
Joined: Jan 2003
Posts: 59
culver city,calif. usa
someone might think that the switch being off means that there is no energy at the assembly. ouch!


#85721 - 07/31/03 11:47 PM Re: Paddle Fan Motor Disconnect ?  
Brian Roberts  Offline
Junior Member
Joined: Jul 2003
Posts: 5
The same thing could be said of an ordinary ceiling light with the feed in the ceiling box. When the light switch is off, a homeowner/DIY could think it's safe to work on. (same "ouch")!


#85722 - 08/01/03 07:07 AM Re: Paddle Fan Motor Disconnect ?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I guess the thread about the disconnecting means for the attic ventilating fan got me wondering if the same issue applies to paddle fans.
Is a paddle fan an appliance?
What is a typical HP rating?
Does 422.32 apply?
What about 430.109(6)(C)?
I know this may seem a bit much, but it is a motor.


#85723 - 08/01/03 11:00 AM Re: Paddle Fan Motor Disconnect ?  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
Redsy,

I've done this type of installation more times than I can remember, but never thought twice about it. I had been trying to find some hp ratings for these motors, but no luck yet, but I've seen .9 amp ratings so I'd guess they're less than 1/8 hp anyway.

Bill


#85724 - 08/01/03 03:51 PM Re: Paddle Fan Motor Disconnect ?  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Have not seen a horspower rating on a residential cieling fan instructions sheet. [Linked Image]


ed

#85725 - 08/01/03 11:27 PM Re: Paddle Fan Motor Disconnect ?  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
I think they are "Fractional / Fractional" HP Motors [Linked Image]

Would imagine the HP rating on the commonly used PSC motor for those ceiling fans is like 1/16 HP at best!

Any more than that would prove to be LETHAL if someone stuck their head up high enough to engage the blades!
(Brings back memories of the '70s classic horror movie - "Dawn of the Dead").

Hands and Fingers would be lossed at an alarming rate!

Also, it would move so much Air at high speed, the effect would be annoying rather than pleasant!

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#85726 - 08/07/03 04:54 PM Re: Paddle Fan Motor Disconnect ?  
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Even if you held a ceiling fan to the most strick motor disconnect rules, the type of fan you are refering to always has a switch on the unit to shut off the fan (otherwise the fan would run constantly without a wall switch). Listed pieces of equipment are allowed to have a unit-mounted, factory-installed switch count as a motor disconnect. So since the disconnect doesn't have to be separate from the unit on larger scales then why do you figure a small unit might need it?


Page 1 of 2 1 2

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 15 (0.004s) Memory: 0.8149 MB (Peak: 0.9887 MB) Zlib enabled. Server Time: 2017-03-25 11:42:29 UTC