The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 307 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85635 - 07/25/03 11:00 AM Working space around transformers
steve66 Offline

Registered: 03/13/03
Posts: 25
Does the working space in Article 110.26 apply to transformers? Would a 480V panelboard across the isle from a 480 to 208 transformer require 4' between them? Also, do the working space requirements apply to the sides of the transformer? If not, how much space would required on the sides to run conduit in and pull wire (aren't transformers usually fed with a LB into to side?) I am laying out an electrical room, but I'm not an electrician, and I'm not sure how the connections to transformers are usually made.

Finally, can the transformer be backed right up aginst a wall, or does it need breathing room behind it?

2014 / 2011 NEC & Related Books and Study Guides
#85636 - 07/25/03 12:13 PM Re: Working space around transformers
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
99NEC 450-9. Transformers with ventilating openings shall be installed so that the ventilating openings are not blocked by walls or other obstructions. The required clearances shall be clearly marked on the transformer.

110-16 working clearances would not be modified by ventilation clearances.

#85637 - 07/25/03 08:17 PM Re: Working space around transformers
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
450.13 Accessibility.

All transformers and transformer vaults shall be readily accessible to qualified personnel for inspection and maintenance ...
Joe Tedesco, NEC Consultant

#85638 - 07/26/03 04:33 AM Re: Working space around transformers
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Working clearances are required to perform preventative maintenance on the xfmr. Granted that most PM can be done with the xfmr not energized, but some will be done live (such as infrared measurements). You will need at least condition 2, possibly condition 3 depending on the interpretation of the AHJ.

[This message has been edited by Ron (edited 07-26-2003).]