ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#85631 - 07/24/03 08:11 PM Sub Panel
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I have a sub panel and all the circuits are in a damp location. Can I feed the sub with a 2-pole GFCI Breaker.
Top
2017 / 2014 NEC & Related Books and Study Guides
#85632 - 07/25/03 03:54 AM Re: Sub Panel
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
What are the circuits?
Do they all need GFCI protection?
If a ground-fault occurs on one branch circuit, it will take out the whole subpanel.
Probably not a desirable design consideration.
Top
#85633 - 07/25/03 01:46 PM Re: Sub Panel
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
The circuits are in the basement and garage. This would not cause a huge problem for the person. The sub panel is in the basement.I was just wondering about code. Does this break any code I can not find the answer.

[This message has been edited by Sparks30 (edited 07-25-2003).]
Top
#85634 - 07/28/03 01:52 PM Re: Sub Panel
rlrct Offline
Member
Registered: 07/03/03
Posts: 26
Loc: South Windsor, CT
From a homeowner's perspective, I can only think of 2 minor reasons to GFI protect the whole subpanel and that's to save a little time or money. I can think of several reasons not to GFI protect a sub.

First, sections 210-8(a)(2,5) have specific exceptions for appliances. The classic example of such an appliance is a freezer. I'd be really unhappy if a receptacle in my garage tripped the GFI breaker and took out a freezer in the basement.

Second, let's say I set up a workshop in either the basement or garage with dedicated circuits for tools/machinery and a separate circuit for lighting. I wouldn't want a GFI trip on a tool to take my lights out.

Third, placing the GFI protection that far "up circuit" from the receptacles could make it more diifficult to troubleshoot nuisance trips. It certainly doesn't seem intuitive to me that an entire panel would be protected. I'd go looking for a hidden GFI feed-through before I thought to check for a GFI breaker feeding the sub (and that's with a GFI breaker for our spa).
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals