#8562 - 03/27/02 01:58 PM Emergency ballast
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
I am doing a very large lighting system and many of the fixtures are NM which represents 'emergency ballast'. They are to be wired before the contactor. Now doesa this mean the ballast has some sort of backup to keep the light illuminated in case of power failure?
Top
Work Gear for Electricians and the Trades
#8563 - 03/27/02 02:24 PM Re: Emergency ballast
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
Don't know the meaning of the acronym "NM", but if your fixtures are controlled by a contactor, then the fixtures that need to have emergency lighting must have battery backup somewhere. Battery packs can be installed on fluorescent fixtures easily. HID fixtures usually use a quartz lamp on a battery. Or they may all be on an emergency generator which will, by Code be up and running within 10 seconds.
Hope this helps.
Top
#8564 - 03/27/02 02:32 PM Re: Emergency ballast
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
NM is just the way the emergency fixtures are identified on the print. I know what you are talking about with the HID's, I have used them. But the customer is ordering all the fixtures because they are a engineering/architect design firm and they wanted to get the fixtures themselves because this is what they do. Any way, the person I went over the job with said these 'NM' fixtures have emergency ballasts. The print also states that these fixtures are to be provided with 'emergency ballasts'
Top
#8565 - 03/27/02 06:08 PM Re: Emergency ballast
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Your fixtures are going to have battery back up. The battery requires a non-switched supply fed from the same circuit feeding the fixture. When the battery loses power it kicks in to supply the lamps for a specified period of time. These fixtures can be wired either as night lights or so they turn off with the lighting control.
Top
#8566 - 03/27/02 06:51 PM Re: Emergency ballast
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
I've installed EM ballasts for a restaurant, and the addition of the red ballast and a test switch and indicator light was all there was to it. I'm guessing the red EM ballast has a battery pack built in it...

Interestingly enough, the directions said to cut the "common" (neutral) with the momentary test switch for testing purposes.

I also remember that they were expensive beasts too...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#8567 - 03/28/02 06:48 PM Re: Emergency ballast
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Run the EM fixtures off of the same light circuit as the lights in that room. Pick it up ahead of the switch. The fixture itself can be switched or not, but you"ll have to have a continuous supply to the EM ballast.
Top
#8568 - 03/28/02 07:02 PM Re: Emergency ballast
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
_________________________
Ron
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals