The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85590 - 07/18/03 01:50 PM Missing something?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A 600 240 volt 3phase service disconnect feeds a wireway that supplies several feeder disconnects.
One of the feeders supplies a wireway, with the conduit acting as EGC.
The wireway supplies 4 disconnects that feed 4 breaker panels via SER cable.
In each disconnect, the grounding conductor and neutral from the SER are connected together to the neutral lug, which is floating (not bonded).
All passed inspection.
What am I missing?

Top
2014 / 2011 NEC & Related Books and Study Guides
#85591 - 07/19/03 05:10 AM Re: Missing something?
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Redsy
You did not miss a thing, the inspector and the contractor both missed something.
I am a Grounding and Bonding nut,and one of my friends loves to say "grounding and bonding are overrated". We both get a good laugh, seems the contractor and the AHJ also got a good laugh.

Pierre
_________________________
Pierre Belarge

Top
#85592 - 07/19/03 05:25 AM Re: Missing something?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Take a look at 250.142 A & B. Also, 310.4, which will go away when you correct the connection between the grounding conductor & the grounded conductor.

Also, how are the disconnects grounded? If they are fed by SER cable, the needs to be a connection to the grounding conductor.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#85593 - 07/20/03 06:46 AM Re: Missing something?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thanks,Guys.
Tom,
The disconnects are grounded via grounding locknuts. The voltage is 240, and no remaining KO rings exist, so that is sufficient. A grounding lug would have done the job correctly.
The thing that puzzles me is that, if the neutral & ground are isolated in the panelboards (I haven't looked yet), and the Neutral/Ground connection is floating in the disconnect enclosure, where is the parallel path for neutral current.
I will try to draw & post a diagram(eventually).

BTW,
This is in the basement of a restaurant.
Shouldn't SER cable should be prohibited?

Top
#85594 - 07/21/03 05:02 AM Re: Missing something?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
If the neutral & the ground are connected to the same lug and or busbar at both ends, that is your parallel path.

There is nothing I know of in the NEC that would prohibit the use of SER cable in a restaurant, prior to the adoption of the 2002 NEC, and even then it would depend on the type of construction used and how the cable is installed. See 338.10(B)(4) and 334.10(3)
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#85595 - 07/21/03 06:05 AM Re: Missing something?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Tom,

A restaurant would be considered a Place of Assembly (Article 518).
Wiring methods, generally, need to be Metal Raceways or MC cable (518.4 (A)).
I guess the basement ceiling/restaurant floor could be non-fire rated? (518.4 (B)).

[This message has been edited by Redsy (edited 07-21-2003).]