LANDSCAPE LIGHTING USING PVC: 120 volt 20 amp GFCI protected: 12 inches (plus) depth: Lights in lawn aside concrete walkway:

Question: Do sweeps and risers to boxes at grade need to be rigid metallic (galvanized)?

Many thanks, Ron
Top
2017 / 2014 NEC & Related Books and Study Guides
#85540 - 07/12/03 06:06 PM Re: Landscape Lights In Pvc
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Are you referring to possible physical damage? per 352.12(C)?
Top
#85541 - 11/04/03 05:07 PM Re: Landscape Lights In Pvc
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
I Can't use PVC where I'm at, (Galvy Only!)but out of town in other cities in my area... Direct burial romex, sleaved with PVC, or just PVC all the way. Then, I dig, ( Or, should I say, have some of the generals guys dig. )a post hole at each light location. Mount my box to a pressure treated 2x4, with a 45 at the top. Looks nice, like it was supposed to be there! Then have the general fill the post hole with concrete, around the 2x4, and the sleeve or conduit. Once the concrete is dry, it is a solid unit! Sounds like a bit too much, but practically in-destructable. You have to run over it with a truck!

But, to answer your question. You still need to support the box, and it depends on what is allowed in your area. Call your Inspector.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#85542 - 11/06/03 02:56 AM Re: Landscape Lights In Pvc
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Q on that e57, could each box be buried ?
Top
#85543 - 11/06/03 03:15 AM Re: Landscape Lights In Pvc
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Ron if you want to support a box holding a fixture with the raceway it must be with rigid and you must follow the rules of 314.23(F)

Quote:
314.23(F) Raceway Supported Enclosures, with Devices, Luminaires (Fixtures), or Lampholders. An enclosure that contains a device(s) or supports a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 450 mm (18 in.) of the enclosure.


If you want to stay with PVC you will have to support the box some other way.

And then of course the inspector could get you on exposed to physical damage as Redsy has pointed out.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals