The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 88 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85539 - 07/12/03 04:29 PM Landscape Lights In Pvc
Ron100 Offline
Junior Member

Registered: 07/12/03
Posts: 1
Loc: Burlingame, CA, USA
LANDSCAPE LIGHTING USING PVC: 120 volt 20 amp GFCI protected: 12 inches (plus) depth: Lights in lawn aside concrete walkway:

Question: Do sweeps and risers to boxes at grade need to be rigid metallic (galvanized)?

Many thanks, Ron

2014 / 2011 NEC & Related Books and Study Guides
#85540 - 07/12/03 06:06 PM Re: Landscape Lights In Pvc
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Are you referring to possible physical damage? per 352.12(C)?

#85541 - 11/04/03 05:07 PM Re: Landscape Lights In Pvc
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
I Can't use PVC where I'm at, (Galvy Only!)but out of town in other cities in my area... Direct burial romex, sleaved with PVC, or just PVC all the way. Then, I dig, ( Or, should I say, have some of the generals guys dig. )a post hole at each light location. Mount my box to a pressure treated 2x4, with a 45 at the top. Looks nice, like it was supposed to be there! Then have the general fill the post hole with concrete, around the 2x4, and the sleeve or conduit. Once the concrete is dry, it is a solid unit! Sounds like a bit too much, but practically in-destructable. You have to run over it with a truck!

But, to answer your question. You still need to support the box, and it depends on what is allowed in your area. Call your Inspector.
Mark Heller
"Well - I oughta....." -Jackie Gleason

#85542 - 11/06/03 02:56 AM Re: Landscape Lights In Pvc
sparky Offline

Registered: 10/18/00
Posts: 5545
Q on that e57, could each box be buried ?

#85543 - 11/06/03 03:15 AM Re: Landscape Lights In Pvc
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Ron if you want to support a box holding a fixture with the raceway it must be with rigid and you must follow the rules of 314.23(F)

314.23(F) Raceway Supported Enclosures, with Devices, Luminaires (Fixtures), or Lampholders. An enclosure that contains a device(s) or supports a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 450 mm (18 in.) of the enclosure.

If you want to stay with PVC you will have to support the box some other way.

And then of course the inspector could get you on exposed to physical damage as Redsy has pointed out.
Bob Badger