#8552 - 03/26/02 09:33 AM Prefered method for underground SE's or feeders
grouser Offline
Junior Member
Registered: 02/11/02
Posts: 4
Greetings from a first time poster. I would like to hear some opinions on your prefered methods for running an underground service or feeder to a subpanel such as to a pole building or other out-building. Do you prefer 3 wire or 4 wire when you have a choice? Do you use a cable assembly or run individual conductors in conduit? What type of cable or conductors? CU or AL. I hear many different arguements on this one here in central Michigan, particularly on when you need 4 wire vs. 3 wire. Thanks for any input, Ed.
Top
Work Gear for Electricians and the Trades
#8553 - 03/26/02 09:55 AM Re: Prefered method for underground SE's or feeders
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
I prefer to use a 4 wire installation. It will remain in complince should a conductive path be established between both buildings sometime in the future.

I have rarely had to replace an underground feeder that was installed in a raceway. I have replaced or repaired quite a few direct buried cables, usually type USE, not UF. I think it usually comes down to workmanship (not nicking the insulation & making sure the first 6" of backfill is free of rocks). I'll personally stick with single conductors in a raceway.

Most folks will jump on the savings offered by Aluminum. Since I'm the one doing the pulling, I like it also. Workmanship is very important with Aluminum conductors. I haven't had any failures that I know about.



[This message has been edited by Tom (edited 03-26-2002).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#8554 - 03/26/02 11:43 AM Re: Prefered method for underground SE's or feeders
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
What size feeders are you talking about?
I believe it is preferrable to run 4 wires and use a raceway. Just because something is acceptable, doesn't mean it is good design for considerations of maintenance and reliability.
Top
#8555 - 03/26/02 04:32 PM Re: Prefered method for underground SE's or feeders
grouser Offline
Junior Member
Registered: 02/11/02
Posts: 4
Feeders would be sized for say a 60A. to 150A.load center or anything in between.
Top
#8556 - 03/26/02 07:34 PM Re: Prefered method for underground SE's or feeders
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
At that size, unless your running hundreds of feet, I can't think of any compelling reason, cost-wise, not to use 4 copper conductors in a raceway (possibly even oversizing the raceway for future considerations).

[This message has been edited by Redsy (edited 03-27-2002).]
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals