The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#85515 - 07/12/03 04:46 AM Raintight EMT
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I've just found out that EMT compression fittings, which I've always considered to be "raintight," aren't listed for that use at this time.
Has anyone stopped using them for this purpose???...S

Top
2014 / 2011 NEC & Related Books and Study Guides
#85516 - 07/12/03 06:56 AM Re: Raintight EMT
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Not me. What are we supposed to do, use GRC or make an ugly looking PVC installation?

I've torn out quite a few outdoor EMT installations & I don't recall seeing any evidence that the connectors & couplings leaked. Of course, one man's experience is limited & this could be a real problem elsewhere.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#85517 - 07/12/03 08:16 AM Re: Raintight EMT
NJwirenut Offline
Member

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
I use them outdoors, as well, and have never had a problem or been red-tagged by an inspector for it.

On a vertical run (like a service riser), I will often smear a bit of RTV around the top compression nut as added insurance against leaks.

Top
#85518 - 07/12/03 08:55 AM Re: Raintight EMT
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Since this came about, I have wondered what caused UL to rescind it's original listing of these fittings. It seems like this could be a credibility awakening for some of their other listings.

I mean, why did this just happen out of the blue, did they decide they had low water pressure the day they originally tested these way back when?

Roger

Top
#85519 - 07/12/03 12:17 PM Re: Raintight EMT
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
This may be old information, but http://tnbelectricalworld.tnb.com/contractor/docs/tbhazardous.pdf seems to call out raintight up to 2 inch, but a few other catalogs do not.

2½-4 inch compression-ring EMT fittings have generally not been raintight listed. A notable exception were fittings for 2½-4 inch EMT so marked, and furnished with a plainly visible rubber boot.

There are a number of ‘raintight’ hits in http://www.steelconduit.org/pdf/ConGuide4.3.pdf

Top
#85520 - 07/12/03 06:09 PM Re: Raintight EMT
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Bjarney, Currently UL does not list any EMT fittings as raintight..Looks like we're all in a heck of a lot of trouble.
This is ridiculous. Failures are generally caused in the terminations...S

Top
#85521 - 07/12/03 06:29 PM Re: Raintight EMT
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
I agree with Tom. PVC can get pretty seedy looking outside on a building surface.

Don't "W-" and "W-2"-rated conductors buy you anything used outdoors?

Top
#85522 - 07/12/03 07:59 PM Re: Raintight EMT
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
 Quote:
Currently UL does not list any EMT fittings as raintight


I thought EMT was not listed for outdoor use--only "rigid" conduit?

Top
#85523 - 07/13/03 06:32 AM Re: Raintight EMT
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Go here for UL's report.
http://www.ul.com/regulators/raintight.html

Roger

Top
#85524 - 07/14/03 06:59 AM Re: Raintight EMT
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Does any one know what part of the connector failed? The connector to box? or the connector to conduit?

Thomas and Betts technical support said that the use of a seperate sealing washer would be suffcient to meet the raintight requirements.