The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (aussie240), 177 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85512 - 07/11/03 09:29 PM Hot tub wiring in detached garage
Brian Roberts Offline
Junior Member

Registered: 07/11/03
Posts: 5
I need to install a typical self-contained hot tub rated 120/240v 50amps in a detached garage. There already exists a 60amp,
3 wire service from the house that feeds a sub panel to supply an air compressor and welder as well as lighting. No power tools will be used when the hot tub is in use. My question is since the 60 amp feeder contains only 3 conductors,
can I add another #6 thwn and add a separate ground bar in the sub panel and then, feed conduit from there to the hot tub service disconnect? Or should I leave the existing sub panel alone and then run a completely new, separate conduit (with all #6THWN) from the main house panel to the garage and feed to the disconnect for the hot tub?
Note that the hot tub & disconnect will be in a separate room of the garage. The existing sub panel is in the main part of the garage.
Thanks for any help on this.

Top
2014 / 2011 NEC & Related Books and Study Guides
#85513 - 07/13/03 07:28 AM Re: Hot tub wiring in detached garage
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Go with the new panel. The inspector might not let you come off the existing subpanel, since you have no way to interlock the power tools with the hot tub. You would also have to get that new conductor in the same raceway as the existing, if you could.
You are better off running new.
_________________________
Ron

Top
#85514 - 07/13/03 06:50 PM Re: Hot tub wiring in detached garage
Brian Roberts Offline
Junior Member

Registered: 07/11/03
Posts: 5
I was under the impression that the NEC prohibits more than one service to a detatched residential garage. How about if I re-install the existing subpanel with 4 THWN copper #6, and then run conduit to the back room for the hot tub disconnect. We can disconnect the compressor & welder since the new owners have no use for them. Thanks for your help.

Top