The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (geoff in UK), 202 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85494 - 07/10/03 06:28 AM 2 SDS in 1 j-box
Cindy Offline
Member

Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
i found a 277v b.c. coming from a building into a parking lot ground box that feeds part of the lighting, and another 277v b.c. coming from a building across the parking lot feeding other lighting... both in the same ground box. what code section does this violate, if it does? and what could be done to fix this? put a barrier in the box? identify each circuit with tags saying which building the power comes from?

Top
2014 / 2011 NEC & Related Books and Study Guides
#85495 - 07/10/03 01:26 PM Re: 2 SDS in 1 j-box
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Cindy,
I don't think that there is a code rule that would prevent this installation or require separation. Maybe you could stretch the definition of "structure" and call the junction box a "structure" and then 225.30 would limit you to one source, but if the box is a structure, then 225.31 would require a disconnect.
Don
_________________________
Don(resqcapt19)

Top
#85496 - 07/10/03 09:41 PM Re: 2 SDS in 1 j-box
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Cindy

I will look to see if there is any 'code violation', I am not sure.

But in answering your question on what to do to fix it, I would at least tag the sets separately with a 'very permanent' method noting that they are fed from different buildings! Who knows what the potential difference between the 2 sets really is.
Even if this is not code, as has been mentioned many times before, code is the minimum necessary to pass an inspection.
Pierre
_________________________
Pierre Belarge

Top