#85479 - 07/07/03 09:42 PM PVC Wet location??
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
I hdd a subpanel feed about 60 feet under ground in PVC. Inspector did not pass because the 2-3 that was pulled through the PVC not wet location rated. Is the inside of the PVC wet location??

Edward
_________________________
Thanks
Edward
Top
2017 / 2014 NEC & Related Books and Study Guides
#85480 - 07/07/03 10:46 PM Re: PVC Wet location??
stamcon Offline
Member
Registered: 03/24/01
Posts: 329
Loc: So San Francisco CA
Edward, from the 99 NEC Article 100-Locations- "Wet Locations. Installations underground or in concrete slabs or masonry in direct contact with the earth, and locations subject to saturation with water or other liquids, such as vehicle washing areas, and locations exposed to weather and unprotected."
If it's in the ground, it's a wet location.
Top
#85481 - 07/08/03 01:59 AM Re: PVC Wet location??
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
From the 2002 NEC

Quote:

300.5(D)(5) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.


And the definition of Wet location is the same as stamcom put up from the 99 code.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#85482 - 07/08/03 02:58 AM Re: PVC Wet location??
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
Edward
Alot of the conductors today come with a THHN/THWN rating, where the rating of the conductor is 90 degrees (column 3, table 310.16) if you use it as THHN, or 75 degrees (column 2, table 310.16) if you use it for THWN. The THWN is permitted for wet locations at 75 degrees. I am curious as to what conductor type you did use?

Pierre
_________________________
Pierre Belarge
Top
#85483 - 07/08/03 06:40 AM Re: PVC Wet location??
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
To add to comments already posted… In many regions, underground raceways breath and accumulate moisture, no matter how much “sealing” is attempted. If “2-3” is a multiconductor cable, it’s unlikely that the individual conductors (or the outer cable jacket) are labeled for wet locations—like you would find with XHHW or USE/RHW conductors.
Top
#85484 - 07/11/03 04:48 AM Re: PVC Wet location??
pip Offline
Member
Registered: 12/13/00
Posts: 15
Loc: Little Elm,Tx
The only way to keep water out of any conduit
with fitttings underground is to pressurize it. I live in dallas,tx and have never pulled wire out of an exsiting conduit underground that was not completely full of water.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals