#85421 - 07/02/03 10:14 AM Spa Light & Recept
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Wiring an outdoor spa with an enclosed Gazaebo around it and unclear at the distances for the GFI protected light (using GFI breaker) over head and recept on the wall. Checking the code, looks to be 5 feet form waters edge on the recept and 7"6" for the light unless a weatherproof light is used.
Any clearer answers to this?
Thx,
Al D
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
2017 / 2014 NEC & Related Books and Study Guides
#85422 - 07/02/03 04:26 PM Re: Spa Light & Recept
DJF Offline
Member
Registered: 05/06/03
Posts: 17
AHJ in one of the counties I work in says a Gazebo is still an Outdoor installation
Top
#85423 - 07/02/03 09:30 PM Re: Spa Light & Recept
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
This one is completely enclosed from the weather and has a sliding door.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#85424 - 07/02/03 09:50 PM Re: Spa Light & Recept
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Al,

This may be a good question for your local AHJ.


My understanding is:
If it's considered inside and the fixtures will be less than 7'6" above Tub they have to be GFCI protected and Non-Metallic (or Metallic isolated from contact) per 680.43(B)(1)(c)(2)

Note that the 7'6" is the height above Maximum Water Level, not from the floor.

Bill
Top
#85425 - 07/02/03 10:03 PM Re: Spa Light & Recept
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
So, 5 ft from the waters edge above should be ok as long as it is GFI protected and non-metallic, assuming the gazebo is weather tite. Liquid-tite and plastic boxes should work, correct?
We don't get much rain here in AZ anyway.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#85426 - 07/03/03 11:11 AM Re: Spa Light & Recept
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
Quote:
NEC 2002 IV. Spas and Hot Tubs 680.43 Indoor Installations.
(c) Below 2.3 m (7 ft 6 in.). Luminaires (lighting fixtures) meeting the requirements of item (1) or (2) and protected by a ground-fault circuit interrupter shall be permitted to be installed less than 2.3 m (7 ft 6 in.) over a spa or hot tub.
(1) Recessed luminaires (fixtures) with a glass or plastic lens, nonmetallic or electrically isolated metal trim, and suitable for use in damp locations
(2) Surface-mounted luminaires (fixtures) with a glass or plastic globe, a nonmetallic body, or a metallic body isolated from contact, and suitable for use in damp locations.


Hope this helps.
Dave
_________________________
Dave
Top
#85427 - 07/07/03 09:41 PM Re: Spa Light & Recept
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
It says the fixture must be non-metallic, does that mean I can't run BX cable or flexible conduit to it?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#85428 - 07/08/03 07:40 PM Re: Spa Light & Recept
John Steinke Offline
Member
Registered: 04/03/01
Posts: 518
Loc: Reno,Nv., USA
I would submit that an enclosed hot tub is a wet location, just as if it were outside, in the open. I say this because a hot tub is, well, hot, and the hot water will condense on everything- including the inside of your fixtures.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 46 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals