The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 340 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85386 - 06/26/03 02:38 PM PVC Expansion joints
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
In the postings about chain link fences, Don made a mention about expansion joints, and it got me to thinking (I know that's a dangerous proposition with me).

Here's the situation- it is a common practice in this area to run schedule 40 pvc along the frame under a mobile home for the feeder supplying the home. Some of these runs can be 50 to 60 feet long. It can get 90 degrees in the summer and as cold as -20 to -30 in the winter for a temperature swing of 110 to 120 degrees. I've never seen an expansion fitting installed in this case

In the example above, the nipple coming down from the panel cannot move & the conduit emerging from the ground into an LB is secured.

Does this installation need an expansion fitiing?
Few things are harder to put up with than the annoyance of a good example.

2014 / 2011 NEC & Related Books and Study Guides
#85387 - 06/28/03 02:06 PM Re: PVC Expansion joints
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
Yes that installation does require an expansion joint. The rule would require an expanison joint for any conduit over 10' long with a 65┬░ change in temperature. A 125┬░ change would require an expansion joint for a 5' run.

#85388 - 06/29/03 05:49 AM Re: PVC Expansion joints
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
In support of Don

The reference to the 2002 NEC is 352.44 and 352.44 Table A. For those who might want the code reference.

Pierre Belarge