#85330 - 06/20/03 03:51 PM Habitable room?
Jim M Offline
Member
Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
I have a job to wire a therapy tub in a single family dwelling. The tub will be set in a deck enclosed by a glass lean-to enclosure. Access will be from the bedroom via french doors. The room will have hvac.

Does this meet the definition of a habitable room? If so how would the prohibitions about receptacle distances from the tub play into the 6/12 spacing? Example, the tub will only be about 2' from the enclosure in some parts.

This will be under the 93 Code if it makes a difference. Any references would be appreciated.

TIA

Jim
Top
2017 / 2014 NEC & Related Books and Study Guides
#85331 - 06/20/03 06:33 PM Re: Habitable room?
stamcon Offline
Member
Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
Jim, you need to find out what Building Code the house falls under. The Uniform Building Code defines a habitable space as "space in a structure for living, sleeping, eating or cooking. Bathrooms, toilet compartments, closets, halls, storage or utility space, and similiar areas, are not considered habitable space."
I would think, habitable or not, the electrical requirements for areas near a tub, etc, would be enforced over 6/12 spacing.

[This message has been edited by stamcon (edited 06-20-2003).]
Top
#85332 - 06/22/03 12:28 AM Re: Habitable room?
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8560
Loc: SI,New Zealand
Jim,
I would say that as long as the receptacles could not be accessed by people that were in the tub, it should be OK.
Is there going to be allowance for GFCI protection on these circuits?, if not, there should be!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#85333 - 06/24/03 10:19 AM Re: Habitable room?
steve66 Offline
Member
Registered: 03/13/03
Posts: 25
The NEC handbook states that "Chapters 5-8 modify chapters 1-4". 680.43 states that outlets can't be closer than 5' to a spa or hot tub. This modifies the rule requiring outlets every 12'.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
1 registered (Admin), 86 Guests and 17 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/07/00
Posts: 3188

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals