#85259 - 06/14/03 04:22 AM How to Recognize a "Terminal Bar"
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
A "terminal bar" used for the termination of equipment grounding conductors is shown here on the right side of this cabinet.

This cabinet encloses a panelboard, and is usually called a "subpanel," and the panelboard's grounded conductor (neutral concuctor with the white identification) is "isolated" or "floating from the metal cabinet, or so called "can" and the EGC terminal is "BONDED" to the can.

This is a "terminal bar" and this is where the EGC's are to be secured under each terminal, some of which may only allow two of the same size per terminal.

The panelboard cover will include this information.

Quote:
408.20 Grounding of Panelboards.

Panelboard cabinets and panelboard frames, if of metal, shall be in physical contact with each other and shall be grounded.

Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet.

The terminal bar shall be bonded to the cabinet and panelboard frame, if of metal; otherwise it shall be connected to the grounding conductor that is run with the conductors feeding the panelboard.



[This message has been edited by Joe Tedesco (edited 03-31-2005).]
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#85260 - 06/14/03 05:13 AM Re: How to Recognize a "Terminal Bar"
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Joe, if someone needs to look at the cover on the panel in order to "recognize a terminal bar" and determine which is for the grounding conductors and which is for the grounded conductors do you think they should be in the panel in the first place?

Not to say the labeling is unimportant but this is some basic electrical knowledge.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#85261 - 06/14/03 05:19 AM Re: How to Recognize a "Terminal Bar"
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
What is the black wire connected to the white wire? If this is a shunt trip the colors are not right.

Roger
Top
#85262 - 06/14/03 05:34 AM Re: How to Recognize a "Terminal Bar"
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
iwire

Exactly, I posted this message and the images from my gallery just for that reason because some people are not sure of what was meant by a "terminal bar" and with 408.20 in mind this is offered to clear up the confusion.

Too many are under the impression that the rules for boxes in 250.148 is applied in a panelboard!
_________________________
Joe Tedesco, NEC Consultant
Top
#85263 - 06/15/03 06:53 AM Re: How to Recognize a "Terminal Bar"
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Roger:

I didn't notice that!

Thanks for the reminder!
_________________________
Joe Tedesco, NEC Consultant
Top
#85264 - 06/15/03 07:15 AM Re: How to Recognize a "Terminal Bar"
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Joe, I know I got off topic, but it just caught my eye.

Roger
Top
#85265 - 06/15/03 11:02 AM Re: How to Recognize a "Terminal Bar"
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
I am in agreement with iwires post of 06-14-2003-08:13AM.

It is apparent that many electrical people, including electrical inspectors, do not know the various terminal bars in Service Equipment, or Panelboards supplied by Feeders.

Some seem to know when it is in diagram(s) of circuit(s) but when looking into a panelboard full of wiring they are "lost" as to the identification of the various terminal bars.
Top
#85266 - 06/15/03 01:07 PM Re: How to Recognize a "Terminal Bar"
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
Thanks for the clarification, Joe.
Now, all we need is more exact wording, e.g., "..one or more terminal bars for terminating all non-isolated grounding conductors shall be secured inside the cabinet." This would better represent the actual practice of using multiple terminal bars, as well as specify the apparent intent of landing ALL the non-isolated equipment grounding conductors at the terminal bar.
Anyone have easy access to a panelboard cover that has specific wording that EGC's have to land on the terminal bar? Or, does the wording just specify that the bar is provided for the EGC's (with no mandatory usage implied)?
Top
#85267 - 06/15/03 04:32 PM Re: How to Recognize a "Terminal Bar"
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
OK, I can't resist any longer...
How do you recognize a terminal bar?
By the drunks waiting for their flight!
Top
#85268 - 06/15/03 05:59 PM Re: How to Recognize a "Terminal Bar"
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
LOL Redsy, bless your heart, it's obvious you held that in as long as you could.

Roger
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals