#85256 - 06/13/03 04:22 PM unmetered leg
ccdave Offline
Member
Registered: 01/27/03
Posts: 59
Loc: culver city,calif. usa
with three options for grounding the unmetered leg of a 3 phase service, ground rod, cold water or building, which is the best and safest???????
thanks--dave
Top
2017 / 2014 NEC & Related Books and Study Guides
#85257 - 06/13/03 06:26 PM Re: unmetered leg
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
the most local earth contact available would get my vote.....
Top
#85258 - 06/13/03 08:08 PM Re: unmetered leg
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
You don't have a choice. If there is a metal underground water piping system, you must use it. If there is effectively grounded building steel you must use it. If they both exist, you must use them both. If you have only the water pipe, you must supplement it with a made electrode and comply with the 25 ohm rule in 250.56 for the made electrode.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals