#85224 - 06/10/03 05:47 AM 230.54 (C) Exception
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
At least one online expert insists that the exception does not permit service heads below the point of attachment, only movement AWAY from the point of attachment.
An exception should directly apply to the rule.
The rule in this case is that service heads be ABOVE the point of attachment, so the exception permits otherwise (BELOW the point of attachment).
If the rule was, for example, that service heads be within 12" of the point of attachment, I might agree that the 24" exception would not necessarily permit the haed installed below.

Anyone else?
Top
2017 / 2014 NEC & Related Books and Study Guides
#85225 - 06/10/03 08:35 AM Re: 230.54 (C) Exception
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Redsy,

IMO the words ... "Where it is impracticable to locate the service head above the point of attachment, the service head location shall be permitted ..." should leave no doubt that it could be left up to AHJ interpretation of what is 'practicable'.

Bill
Top
#85226 - 06/10/03 08:43 AM Re: 230.54 (C) Exception
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Assuming that it is agreed that it is indeed impracticable (whatever that may mean in this particular instance).
Does the exception permit you to install the head lower than the attachment point of the service drop.
I say it does.
Top
#85227 - 06/10/03 08:58 AM Re: 230.54 (C) Exception
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
I say it does too.
I can't see it meaning anything else.

Bill
Top
#85228 - 06/10/03 02:23 PM Re: 230.54 (C) Exception
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
The exception is included as a part of the NEC to provide a reference for us AHJ's to modify the rule as written. (A little common sense always helps too) In my area, a discussion with the Utility Co. Wiring Inspector prevents this subject from becoming a nightmare.
John
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 40 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals