#85211 - 06/06/03 06:07 PM 250.104(A)(1)
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
250.104(A)(1) reads:
Quote:
General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) used shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3)
Does this, by itself mean that water piping systems shall be bonded to the service equipment enclosure and the grounded conductor at the service?

Or does it mean bonded to either the service equipment enclosure or the grounded conductor at the service?

Bill
Top
2017 / 2014 NEC & Related Books and Study Guides
#85212 - 06/06/03 06:46 PM Re: 250.104(A)(1)
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Bill, as far as grammar is concerned, (I don't know if you want to listen to me knowing how I did in grammar) items in sequence divided by commas followed by "and" are in addition to. Items in sequence followed by "or" are optional.

Roger
Top
#85213 - 06/06/03 06:56 PM Re: 250.104(A)(1)
txsparky Offline
Member
Registered: 05/25/01
Posts: 552
Loc: Magnolia,.Texas U.S.A.
Roger,
You get an "A+" today !!
_________________________
Donnie
Top
#85214 - 06/06/03 07:30 PM Re: 250.104(A)(1)
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Roger,

I think you're right.
Do you think that was the intent?

Bill
Top
#85215 - 06/07/03 08:48 AM Re: 250.104(A)(1)
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Thanks Donnie. Bill, I would say this was the intent. The part I think should be changed, is "or to the one or more grounding electrodes used". If the GE installation is soley rods and the GEC is #6 we would have a conflict with "the grounding electrode conductor where of sufficient size".

I mean if we bond to the GEC we have to concern ourselves with the size of the GEC but, if we attach to the GE itself the wording would let us ingnore the GEC size.

And on the same point, "The bonding jumper(s) used shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3)" what would this accomplish?

Roger
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals