#85178 - 06/03/03 10:22 AM Code Violations?
boxford Offline
Member
Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
I need some help finding exact articles on how the following application would be a code violation:

A disconnect with one auxiliary contact was ordered for a job. Going to the Disconnect from a control panel was 480VAC, 4/C #12 SH cable for the motor, 2#12 conductors for the disconnect auxiliary contact, and 2#12 conductors for the motor thermal switch. The 2#12's for the disconnect were wired to the auxiliary contact in the disconnect. The 2#12's for the motor thermal switch were wired directly to the mts but were routed through the disconnect. So, when the auxiliary contact for that disconnect is opened it takes out the motor but the motor thermal switch is still live.

Thank you for all of your help.
Top
2017 / 2014 NEC & Related Books and Study Guides
#85179 - 06/03/03 07:25 PM Re: Code Violations?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
The bible is in the truck, and of course it's rainin again.

The disco must open all ungrounded conductors to the equipment. Are the 2-12s for the thermal powered?? If so, then you have to break them when the disco is opened.
John
_________________________
John
Top
#85180 - 06/03/03 09:29 PM Re: Code Violations?
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
NEC 2002 404.15 Marking.
(A) Ratings. Switches shall be marked with the current voltage, and, if horsepower rated, the maximum rating for which they are designed.
(B) Off Indication. Where in the off position, a switching device with a marked OFF position shall completely disconnect all ungrounded conductors to the load it controls.

Hope this helps!
_________________________
Dave
Top
#85181 - 06/04/03 04:50 AM Re: Code Violations?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
A thermal switch is a device, not a load.
Don
_________________________
Don(resqcapt19)
Top
#85182 - 06/04/03 06:50 AM Re: Code Violations?
boxford Offline
Member
Registered: 03/10/03
Posts: 15
Loc: St. Paul, MN, USA
Hotline1,

The motor thermal switch is connected to an I/O module which is at 120VAC. Could you provide me with a code reference?
Top
#85183 - 06/04/03 08:46 AM Re: Code Violations?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Opening the disconnect will not remove the 120 VAC that is provided by the IO module.
Technically, this may not be an NEC violation any more than the presence of 2 voltage sources in any single enclosure, in this case, the peckerhead. However, most electricians probably would assume that if the disconnect is open, there is no voltage present.
At the very minimum, a warning that more than one voltage source is present should be posted somewhere.
Top
#85184 - 06/04/03 02:00 PM Re: Code Violations?
elektrikguy Offline
Member
Registered: 05/25/02
Posts: 132
Loc: woodstock,ga,usa
I agree with redsy.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals