#85073 - 05/27/03 07:40 AM Article 285 TVSSs
txsparky Offline
Member
Registered: 05/25/01
Posts: 552
Loc: Magnolia,.Texas U.S.A.
How often do you see the TVSS double lugged to the main breaker in a panel? I see it pretty regularly

However, in reading 285.21 it sounds as though that doublelugging is required. More specifically 285.21(A)(2)Feeder Supplied Building or Structure
Quote:
The transient voltage surge suppressor shall be connected on the load side of the first overcurrent device at the building or structure.

Do some people interpret this a meaning attached to the first overcurrent device or what? I interpret as meaning downstream of the first device.

[This message has been edited by txsparky (edited 05-27-2003).]
_________________________
Donnie
Top
2017 / 2014 NEC & Related Books and Study Guides
#85074 - 05/27/03 10:15 AM Re: Article 285 TVSSs
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
Tx,

The lugs must be listed for more than one conductor. I agree with your concern.

The TVSS works better when its leads are as short as possible / practical and when they are connected as close as possible / practical to the lowest impedance conductors in the assembly.

I've attended a couple presentations by a local power quality consulting group that cleary demonstrates the benefits of not just slapping the TVSS unit in to "get it hooked up". The best TVSS performance is achieved by reconfiguring the existing hardware enough to provide lugs as close to the main service conductors as practical, and to mount the TVSS unit to keep the leads short.
_________________________
Al Hildenbrand
Top
#85075 - 05/27/03 06:41 PM Re: Article 285 TVSSs
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Tex,
I,m confused. (Not uncommon).
If it is "double-lugged" to the main, wouldn't it likely be on the line side?
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 53 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals