The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85069 - 05/26/03 07:38 AM height above gas pumps considered hazardous location?
jimmyinanniston Offline
Junior Member

Registered: 05/25/03
Posts: 8
Loc: ohatchee,alabama,usa
What is the height above gas pumps considered hazardous location?
_________________________
jimmy w. brown

Top
2014 / 2011 NEC & Related Books and Study Guides
#85070 - 05/26/03 11:11 AM Re: height above gas pumps considered hazardous location?
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
If it's a typical dispenser that is on the ground, the classified area stops at the top of the pump housing.

Article 514

Top
#85071 - 06/05/03 06:19 PM Re: height above gas pumps considered hazardous location?
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
I disagree. The "zone" continues up to a point 12 feet from the ground/grade. That's why the lights are always at least a little higher than that- so they don't have to use x-proof fixtures. Of course, it's also nice if a 13'6" semi will also miss them- but changing bulbs is a pain!

Top
#85072 - 06/06/03 07:59 PM Re: height above gas pumps considered hazardous location?
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
John:

I think figure 514.3 in the 2002 NEC clearly shows the classified area stops at the top of the dispenser.

You have a good point about the light fixtures, 514.7 says you have to comply with 511.7.
While you have to comply with this article I think the light fixtures are above the classified area and not in it.

Russ