The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 03:29 PM
Looking for older post
by Texas_Ranger
Today at 03:22 PM
Safety at heights?
by gfretwell
Today at 02:19 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
0 registered (), 77 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#85053 - 05/24/03 03:30 PM Is this a permitted method emt to ac?
wa2ise Offline
Member

Registered: 11/29/02
Posts: 773
Loc: Oradell NJ USA
Is this allowed? Assume that there are no splices in the wires (that the BX sheath was cut several feet into its length and the newly exposed wire now resides in the emt. Also, do I need to keep the cover plate on the pull box accessible after it's installed in the house?

[img}http://home.netcom.com/~wa2ise/power/emt-bx.jpg[/img]

Bob, homeowner who'd like to get it right.

Top
2017 / 2014 NEC & Related Books and Study Guides
#85054 - 05/24/03 03:32 PM Re: Is this a permitted method emt to ac?
wa2ise Offline
Member

Registered: 11/29/02
Posts: 773
Loc: Oradell NJ USA

Top
#85055 - 05/25/03 03:44 PM Re: Is this a permitted method emt to ac?
WebSparky Offline
Member

Registered: 02/21/03
Posts: 144
Loc: Cleveland, Ohio
Quote:
Also, do I need to keep the cover plate on the pull box accessible after it's installed in the house?


Nec 2002
314.29 Boxes and Conduit Bodies to Be Accessible.
Boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building...........

Hope this helps!
Dave
_________________________
Dave

Top
#85056 - 05/25/03 08:56 PM Re: Is this a permitted method emt to ac?
Gabriel Offline
Junior Member

Registered: 05/19/03
Posts: 5
Loc: Cedar Rapids, IA usa
Hello Bob,

Yep-Conduit bodies and covers have to be accesible however if you change that jake-L in your photo to a flex changeover (maybe 1/2 rigid coupling) I believe your good to go
Also, all three items in the photo are approved raceways, I surely haven't ever heard of anything against using all together!

Top
#85057 - 05/26/03 06:04 AM Re: Is this a permitted method emt to ac?
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
If you were to change the pull elbow to a rigid coupling, it doesn't appear that one could see the required anti-short bushing for inspection purposes. The fix for that would be to use the type of AC connector with the small hole through which the bushing can be seen.
I think you're fine as is, provided you make sure it's accessible...S

[This message has been edited by electure (edited 05-26-2003).]

Top
#85058 - 05/26/03 07:26 AM Re: Is this a permitted method emt to ac?
elektrikguy Offline
Member

Registered: 05/25/02
Posts: 133
Loc: woodstock,ga,usa
If the inspector was looking for an antishort all he would have to do is remove the cover and look for the little tail on the antishort. I have used a similar method when roughing in block walls. I would extend 1/2" conduits and 90 at ceiling. One could run mc to the conduit, use a mc/emt connector and strip mc long enough to get to box.

Top
#85059 - 05/28/03 08:30 PM Re: Is this a permitted method emt to ac?
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
Wire that is not a part of a UL approved NEC wiring method is required to be marked with certain information every so many feet. Since wire used in AC cable is typically not marked and only the tag on the AC cable tells you what type and size wire it is, technically I think it may be noncompliant.

Practically I think it is probably ok.

AC cable is not a raceway by the way.

No the short radius elbow cannot be buried.

Top