#85053 - 05/24/03 03:30 PM Is this a permitted method emt to ac?
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
Is this allowed? Assume that there are no splices in the wires (that the BX sheath was cut several feet into its length and the newly exposed wire now resides in the emt. Also, do I need to keep the cover plate on the pull box accessible after it's installed in the house?

[img}http://home.netcom.com/~wa2ise/power/emt-bx.jpg[/img]

Bob, homeowner who'd like to get it right.
Top
2017 / 2014 NEC & Related Books and Study Guides
#85054 - 05/24/03 03:32 PM Re: Is this a permitted method emt to ac?
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
Top
#85055 - 05/25/03 03:44 PM Re: Is this a permitted method emt to ac?
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
Quote:
Also, do I need to keep the cover plate on the pull box accessible after it's installed in the house?


Nec 2002
314.29 Boxes and Conduit Bodies to Be Accessible.
Boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building...........

Hope this helps!
Dave
_________________________
Dave
Top
#85056 - 05/25/03 08:56 PM Re: Is this a permitted method emt to ac?
Gabriel Offline
Junior Member
Registered: 05/19/03
Posts: 5
Loc: Cedar Rapids, IA usa
Hello Bob,

Yep-Conduit bodies and covers have to be accesible however if you change that jake-L in your photo to a flex changeover (maybe 1/2 rigid coupling) I believe your good to go
Also, all three items in the photo are approved raceways, I surely haven't ever heard of anything against using all together!
Top
#85057 - 05/26/03 06:04 AM Re: Is this a permitted method emt to ac?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
If you were to change the pull elbow to a rigid coupling, it doesn't appear that one could see the required anti-short bushing for inspection purposes. The fix for that would be to use the type of AC connector with the small hole through which the bushing can be seen.
I think you're fine as is, provided you make sure it's accessible...S

[This message has been edited by electure (edited 05-26-2003).]
Top
#85058 - 05/26/03 07:26 AM Re: Is this a permitted method emt to ac?
elektrikguy Offline
Member
Registered: 05/25/02
Posts: 132
Loc: woodstock,ga,usa
If the inspector was looking for an antishort all he would have to do is remove the cover and look for the little tail on the antishort. I have used a similar method when roughing in block walls. I would extend 1/2" conduits and 90 at ceiling. One could run mc to the conduit, use a mc/emt connector and strip mc long enough to get to box.
Top
#85059 - 05/28/03 08:30 PM Re: Is this a permitted method emt to ac?
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
Wire that is not a part of a UL approved NEC wiring method is required to be marked with certain information every so many feet. Since wire used in AC cable is typically not marked and only the tag on the AC cable tells you what type and size wire it is, technically I think it may be noncompliant.

Practically I think it is probably ok.

AC cable is not a raceway by the way.

No the short radius elbow cannot be buried.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals