The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#84991 - 05/22/03 07:34 AM Green or Green With Yellow Stripe for EGC Only!!
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
The 2005 NEC will include a new requirement stating that green insulation or green with a yellow stripe are only permitted to be used for the identification of the equipment grounding conductor.





[This message has been edited by Joe Tedesco (edited 05-25-2003).]
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#84992 - 05/22/03 09:00 AM Re: Green or Green With Yellow Stripe for EGC Only!!
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
.

[This message has been edited by dana1028 (edited 05-22-2003).]

Top
#84993 - 05/22/03 10:27 AM Re: Green or Green With Yellow Stripe for EGC Only!!
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The proposed wording says that any conductor "identified as permitted" in this section shall
only be used as an EGC. The use of a bare wire is permitted to identify an EGC, this will mean that bare conductors are no longer permitted to be used as grounding electrode conductors.
Don
_________________________
Don(resqcapt19)

Top
#84994 - 05/22/03 10:55 AM Re: Green or Green With Yellow Stripe for EGC Only!!
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Is there a similar proposal for white and white/red colors with grounded-circuit conductors?

The hazards seem similar to those cited by Phil Simmons for green and green/yellow.

Top
#84995 - 05/22/03 12:42 PM Re: Green or Green With Yellow Stripe for EGC Only!!
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Don:

I think that the new sentence makes it clear that the color green or green with a yellow strip will not be allowed to be used to identify the GEC.

The comment stage is where any changes proposed to the original accepted actions can be made by any person who wants to send one in.



[This message has been edited by Joe Tedesco (edited 05-24-2003).]
_________________________
Joe Tedesco, NEC Consultant

Top
#84996 - 05/22/03 12:47 PM Re: Green or Green With Yellow Stripe for EGC Only!!
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
What would we do with all that bare solid larger than #10?

Roger

Top
#84997 - 05/22/03 01:08 PM Re: Green or Green With Yellow Stripe for EGC Only!!
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
So then an exception to the rule above may be in order"

"Exception: Grounding electrode conductors shall be permitted to be bare."
_________________________
Joe Tedesco, NEC Consultant

Top
#84998 - 05/22/03 01:25 PM Re: Green or Green With Yellow Stripe for EGC Only!!
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Who would this change benifit?

Top
#84999 - 05/22/03 01:32 PM Re: Green or Green With Yellow Stripe for EGC Only!!
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
You are correct that the new wording would prohibit the use of green for the grounding electrode conductor. My comment will be to "accept in principle" with the following words added at the end of the proposed wording, "or grounding electrode conductor".
Don
_________________________
Don(resqcapt19)

Top
#85000 - 05/22/03 02:04 PM Re: Green or Green With Yellow Stripe for EGC Only!!
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Why not identify the EGC with green and yellow stripes only and the GEC with green (or bare) only. Then the US would follow the international standard on the EGC identification (I don't think there is a standard for the GEC)