The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Today at 08:46 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 285 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84988 - 05/22/03 06:22 AM cb/disco
engy Offline

Registered: 06/25/02
Posts: 15
Loc: Minnesota
Secondary of a transformer has a 400A switch fused at 225A and feeds a panel in another room. The panel showed up with a 400A main breaker by mistake. At this point the main breaker only serves as a disconnect. Are there any code issues with not changing the main to 225A? Just identify in the panel that the breaker is disconnect only?

2014 / 2011 NEC & Related Books and Study Guides
#84989 - 05/22/03 04:02 PM Re: cb/disco
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Michael, this "sub-panel" actually needs no main breaker. So I wouldn't do anything if not questioned. If it became a major problem, why not remove the breaker and install lugs?


#84990 - 05/23/03 10:16 AM Re: cb/disco
engy Offline

Registered: 06/25/02
Posts: 15
Loc: Minnesota
I thought about removing breaker and installing lugs, but wanted opinions on leaving the main in.