#84979 - 05/21/03 07:59 PM 93 NEC needed
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
I have just started to deal with a jurisdiction that is still using the 93 NEC. I have misplaced my copy in the recent move. If anyone has one that they would like to sell please let me know.

Thanks for not laughing too hard.

Jim
Top
2017 / 2014 NEC & Related Books and Study Guides
#84980 - 05/21/03 08:08 PM Re: 93 NEC needed
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
_________________________
Ron
Top
#84981 - 05/22/03 09:06 AM Re: 93 NEC needed
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
Jim - just so you know...I spotted that eBay '93 a couple of days ago and plan on bidding on it as well. Been looking for a '93 for 'bout a month now.

[This message has been edited by dana1028 (edited 05-22-2003).]
Top
#84982 - 05/22/03 12:55 PM Re: 93 NEC needed
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Guys:
I have a '93 Handbook, McGraw Hill/McPartland; if you're interested.
Probably have a '93 NEC at the shop
If ya want it let me know.
John
_________________________
John
Top
#84983 - 05/22/03 02:20 PM Re: 93 NEC needed
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
John,

I will buy either one, but would prefer the Handbook. Let me know via email.

Thanks,
Jim
Top
#84984 - 05/22/03 03:14 PM Re: 93 NEC needed
rmiell Offline
Member
Registered: 11/09/00
Posts: 242
Loc: La Junta, Co. USA
As a contractor, why worry? Wire according to the 2002 NEC, and it, hopefully, will be in excess of that required in 1993. GFCIs within 6' of kitchen sink? 2002 is more strict. Ampacity of wire? Should be the same. etc............

Anyone think of a rule that would be a problem?

Rick Miell
Top
#84985 - 05/22/03 03:53 PM Re: 93 NEC needed
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
Rick,

I have tried that approach. The head inspector says that to do something that is permitted by a later Code is a legal issue. He feels that it would be breaking the law and he will not open himself nor the inspection department up to a legal challenge. As far as he is concerned there is no Code past the 93.

I just tried to wire a hot tub using NM-B from the panel to the DC then PVC to the tub. No go, conduit all the way from the panel. No room to negotiate even though this would have been Code compliant under the 02.

I also believe that the circuit requirements for bathrooms are significantly different.

[This message has been edited by Jim M (edited 05-22-2003).]
Top
#84986 - 05/23/03 05:56 PM Re: 93 NEC needed
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Rick,
One issue that comes to mind is supporting boxes in t-bar ceilings. If memory serves me correctly, there was a drastic change between the ’96 and ’99 codes. The ’96 required rigid support of boxes and it could not be attached to the ceiling system. The ’99 allowed the use of ceiling wire support provided it was attached to the ceiling system. I don’t have these code books with me to check but that’s how I remember it. This would be a case of the later code making things more lenient and a possible problem with Jim M’s AHJ.
Top
#84987 - 06/01/03 08:09 PM Re: 93 NEC needed
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
Jim,

you can always exceed the code without there being a legal problem. Later codes will not be less stringent than older codes.

Is the inspector going to tell you that you can't install a separate 20 amp circuit for the bathroom because the 93 code doesn't say so?
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals