The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 83 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84943 - 05/18/03 05:37 AM bond bushing
gserve Offline
Member
Registered: 03/11/03
Posts: 92
Do you need a bond bushing when using a offset nipple if 1 end is threaded into a myers hub? The offset nipple is installed between the bottom of a meter socket and the top of a disconnect.
Top
2017 / 2014 NEC & Related Books and Study Guides
#84944 - 05/18/03 04:08 PM Re: bond bushing
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Given the fact that Myers makes a grounding hub, I think that you will need something more than the standard Myers hub. This bonding is only required by the code at one end of the nipple, but some utilities require both ends to be bonded.
Don
_________________________
Don(resqcapt19)
Top
#84945 - 05/18/03 06:18 PM Re: bond bushing
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
If no leftover KOs remain, you can use a grounding locknut. If some remain, a bonding bushing would be required.
250.92(A)
Top
#84946 - 05/18/03 07:22 PM Re: bond bushing
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
Has anyone come up with the final determination on the Myer's hub grounding acceptability for bonding ahead of the main?

I know this was the topic of separate thread, but I never checked to see if anyone came up with a final answer on this.

I wouldn't call the locknut on a Myer's hub a 'standard' locknut. And disregarding concentric KO's the surface area a Myer's hub makes to an enclosure is probably just as much if not more than using a bonding bushing. Not to mention most electricians don't make the connections tightly enough on bond bushings quite often--a mistake less likely and easier to determine during inspection with a Myer's Hub.
Top
#84947 - 05/24/03 06:00 AM Re: bond bushing
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The opening post said

Quote:
"installed between the bottom of a meter socket and the top of a disconnect."


That being the case the nipple contains service entrance conductors, grounding bushings are required regardless of KOs left or not.

2002 NEC
250.92(A)(1) and (2)
250.92(B)(1) and (4)

From the 2002 Handbook regarding
250.92(B)(4)

Quote:
Note that method (4) requires other similar devices, such as bonding-type locknuts or bushings. Standard locknuts or sealing locknuts are not acceptable as the “sole means” for bonding on the line side of service equipment.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#84948 - 05/28/03 08:38 PM Re: bond bushing
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
A bonding locknut can be used for grounding service conduits ahead of the main.

They can't be used if there are KO's left because the angled screw on the locknut sets into the concentric KO's and not a solid piece of metal on the enclosure.

Anyone get an answer from UL or manufacturer yet?

I also would like to mention that a bond bushing will not fit far enough onto the threads of a Myer's Hub in order to properly set the set screw into the threads.
Top
#84949 - 05/28/03 09:49 PM Re: bond bushing
DJF Offline
Member
Registered: 05/06/03
Posts: 17
Steve T
I believe if you re-read the 2nd from top post, you will find your answer to your question concerning bonding the Meyers Hub.

Hope this helps.
Top
#84950 - 06/01/03 07:41 PM Re: bond bushing
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
DJF,

If a company makes more than one type of compliant service bonding method (fitting) it doesn't necessarily mean one is listed for grounding and one is not. I'm sure there are manufacturers who make grounding bushings and grounding locknuts which are both listed fittings.
Top
#84951 - 06/01/03 09:25 PM Re: bond bushing
DJF Offline
Member
Registered: 05/06/03
Posts: 17
Steve T
The point you make is very valid and well taken. I just assumed that resqcapt19 saying "I think that you will need something more than the standard Meyers hub." indicated that the standard Meyers hub was not suitable for Service Equipment bonding.