The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
01/18/17 02:37 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
HotLine1 21
Webmaster 20
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
2 registered (Ruben Rocha, Webmaster), 0 Guests and 208 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84888 - 05/14/03 07:33 PM working clearance
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
This is from another forum -
"Equipment closet that opens to the outdoors, breaker panel mounted standard height off floor, refrigerant lines running at floor level under panel. Inspector says the lines are blocking access to the panel. I can stand at the panel and the lines pass right over my toes. I don't see any access restriction here. Can someone point me to a code reference where panel access is covered? "

If the panel was surface mounted and there was no j-box/LB under the panel, could the wall below the panel be furred out the depth of the panel, thus covering the A/C lines?

110-26 was replied by another poster, but I was just wondering about rectifing the violation, if the lines couldn't be moved.

[This message has been edited by stamcon (edited 05-14-2003).]

Top
2017 / 2014 NEC & Related Books and Study Guides
#84889 - 05/15/03 03:55 AM Re: working clearance
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
110.26(A)(3) requires the working space to extend upward from the floor.
Your solution seems to protect the AC lines, but if the wall was furred out below the panel only, someone could still cite the above NEC reference. I would ask the AHJ first.
Could you box the panel in completely, making it flush?

Top
#84890 - 05/15/03 08:25 AM Re: working clearance
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The installation is in violation of 110.26(F)(1)(a). It is a dedicated equipment space violation, not a work space violation.
Don
_________________________
Don(resqcapt19)