The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (HotLine1), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84853 - 05/12/03 03:50 PM To GFI or not to GFI
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I am wiring a home theater and the equipment will be installed in the basement on a rack. The specs call for two 20 amp isolated ground receptacles. The basement is not finished and the rack will be in front of the receptacles. I am not sure if these are required to be gfi protected under the exceptions to 210.8 A (5). I don't think so but I'd like other opinions. Thanks Scott

Top
2014 / 2011 NEC & Related Books and Study Guides
#84854 - 05/12/03 04:13 PM Re: To GFI or not to GFI
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I would think both exception No. 1 and No. 2 would apply.

 Quote:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(A) Dwelling Units.

(5) Unfinished basements

Exception No. 1: Receptacles that are not readily accessible.

Exception No. 2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8)
.


Isolated ground, isolated from what in a typical residence?

If you run it in NM from a main panel it will be isolated, as long as you don't mount the box to a water pipe.

But if the customer thinks it is better what can you do.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts