The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
01/18/17 02:37 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
HotLine1 21
Webmaster 20
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
2 registered (Ruben Rocha, Webmaster), 0 Guests and 208 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84786 - 05/05/03 05:27 AM Paint shop
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
I have a question We`re putting in some crouse-hines Illuminator fluoresant lighting in a paint shop new area they are sealed and approved for the area.My question is we have a seal where conduit enters new room and the fixture is sealed If there are no connections in the condulets between two seals can they be standard condulets (t`s and lb`s) or would they also have to be rated for the location. Thanks in advance

Top
2017 / 2014 NEC & Related Books and Study Guides
#84787 - 05/05/03 06:11 AM Re: Paint shop
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Is the area Div 1 or Div 2? If Div 1, then 501.4(A)(3) requires explosionproof fittings.
Don
_________________________
Don(resqcapt19)