The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (gfretwell), 321 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84786 - 05/05/03 05:27 AM Paint shop
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
I have a question We`re putting in some crouse-hines Illuminator fluoresant lighting in a paint shop new area they are sealed and approved for the area.My question is we have a seal where conduit enters new room and the fixture is sealed If there are no connections in the condulets between two seals can they be standard condulets (t`s and lb`s) or would they also have to be rated for the location. Thanks in advance

2014 / 2011 NEC & Related Books and Study Guides
#84787 - 05/05/03 06:11 AM Re: Paint shop
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
Is the area Div 1 or Div 2? If Div 1, then 501.4(A)(3) requires explosionproof fittings.