ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#84786 05/05/03 08:27 AM
Joined: Apr 2002
Posts: 178
R
Member
I have a question We`re putting in some crouse-hines Illuminator fluoresant lighting in a paint shop new area they are sealed and approved for the area.My question is we have a seal where conduit enters new room and the fixture is sealed If there are no connections in the condulets between two seals can they be standard condulets (t`s and lb`s) or would they also have to be rated for the location. Thanks in advance

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84787 05/05/03 09:11 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Is the area Div 1 or Div 2? If Div 1, then 501.4(A)(3) requires explosionproof fittings.
Don


Don(resqcapt19)

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5