The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84786 - 05/05/03 05:27 AM Paint shop
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
I have a question We`re putting in some crouse-hines Illuminator fluoresant lighting in a paint shop new area they are sealed and approved for the area.My question is we have a seal where conduit enters new room and the fixture is sealed If there are no connections in the condulets between two seals can they be standard condulets (t`s and lb`s) or would they also have to be rated for the location. Thanks in advance

Top
2014 / 2011 NEC & Related Books and Study Guides
#84787 - 05/05/03 06:11 AM Re: Paint shop
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Is the area Div 1 or Div 2? If Div 1, then 501.4(A)(3) requires explosionproof fittings.
Don
_________________________
Don(resqcapt19)