The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#84740 - 04/30/03 07:08 PM Number of GFI's on ckt
spkjpr Offline
Member

Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
Help, please. I have another of those is it Code or what. I seem to remember there is a maximum number of receptacles that can be downstream fed by a single GFI. Just can't remember if it was in the installation paperwork or the NEC. I have gone blind looking for it in the NEC. Thanks.

Top
2014 / 2011 NEC & Related Books and Study Guides
#84741 - 05/01/03 04:09 AM Re: Number of GFI's on ckt
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
No code issue. Check manufacturers info. I have never done more than a few downstream receptacles so I have never given it much thought. (Or read the instructions!)

Top
#84742 - 05/01/03 05:27 AM Re: Number of GFI's on ckt
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I think this is an old wives tale.
The only reference to problems associated with multiple downstream GFCIs I've ever seen was in the sales literature for a high-end circuit analyzer.

Top
#84743 - 05/01/03 06:49 AM Re: Number of GFI's on ckt
BPHgravity Offline
Member

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
Even though it is not a code requirement, I feel multiple receptacles off of one GFCI is a bad design. Especially when fed to different rooms or locations at an occupancy. There is nothing worse than loosing power at several locations from one nuisance trip. I only feed additional receptacles off of a single GFCI device that are in the immediate vicinity and limit it to two additional receptacles at most. Just my opinion.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#84744 - 05/01/03 06:59 AM Re: Number of GFI's on ckt
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
Some GFI manufacturer's installation instruction have a listed number of receptacles that can be feed from one GFI. I remember 6 on a 15A ckt. It been a while since I read thru those instructions.
Except for bathrooms, any feed thru recepticles, that I install, are in sight of the GFI. JMHO.
_________________________
ed

Top
#84745 - 05/01/03 08:31 AM Re: Number of GFI's on ckt
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
You guys are the best. JMHO

Top
#84746 - 05/01/03 08:50 AM Re: Number of GFI's on ckt
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
There is in fact a limit on the number of appliances you can connect. Unfortunately, it varies from time to time. The background is that a GFCI is extremely sensitive, tripping at a unbalance of just 5mA. Each appliance, or at least those with a equipment ground, "leak" from hot to ground. For example, computers leak about a milliamp on 240V. (I don't know how much it leaks on 120V.) I would not be surprised if some GFCI manufacturers for this reason cite a maximum number of receptacles to bed fed from a single GFCI.

Top
#84747 - 05/01/03 06:25 PM Re: Number of GFI's on ckt
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
For what it's worth...
Spoke to a few "engineers" at a mfg about a similar situation.
First comment was "180 va each"
Second comment was "6 on a 15"; "8 on a 20".
Third was "read the enclosed literature".

I wasn't thrilled at any of the above answers and handed the instructions to the guy who asked the question.
Personally, we keep it "in sight" and no more than two downstream duplexes.
John
_________________________
John

Top
#84748 - 05/01/03 07:11 PM Re: Number of GFI's on ckt
spkjpr Offline
Member

Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
Thanks guys. I am half blind from looking for it in the NEC and now I guess suffering from half-timers, not old enough for old-timers. Thinking it was in manufacturers info, thanks again.

Top
#84749 - 05/01/03 08:38 PM Re: Number of GFI's on ckt
amp-man Offline
Member

Registered: 06/23/01
Posts: 144
Loc: Sacto, California US of A
Another thought--

I've seen tract houses where a single GFI was installed and used to protect receptacles in the bathrooms and the front and back exterior outlets! With maybe 80 feet of cable on the load side of the GFI, with some over-driven plain steel cable staples, the GFI started to nuisance trip as it aged. Even with nothing plugged into any of the protected receptacles.

I think the too-tight staples caused some capacitive coupling from hot to neutral, enough to trip the GFI.

My solution was to install a GFI at each outlet. Wish I'd had a megger then, it would've been interesting to see the extent to which the insulation was compromised.

Cliff

Top
Page 1 of 2 1 2 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals