Are we required to place a grounding bushing on commo raceways (metallic) that stub up through the slab? Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#84727 - 04/29/03 05:34 AM Re: Grounding telephone conduit
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
tmon,
Phone systems are a Chapter 8 installation. The rules in Chapters 1-4 do not apply unless specified in the Chapter 8 article. The only requirement for conduit grounding is on the line side of the primary protector. See 800.12(C). The only requirement (800.48) for interior conduits on the building side of the protector is that the raceway be installed per the Chapter 3 article that applies to that raceway. The grounding requirements for raceways are in Arcle 250, not Chapter 3, so grounding is not required by the code.

[This message has been edited by resqcapt19 (edited 04-29-2003).]
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals