The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84718 - 04/28/03 07:07 AM wires to panel box
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Is there a violation with this:I installed a 200 a panel drilled a 2" hole in floor under panel installed nail plate ran all my circuit wiring through this hole.I also installed a 2" conduit on the bottom also I caped it off under home for future use.The home owner called said the inspector didn`t like all the wires coming through the hole and the abandon pipe installation.She said he left no code numbers of violation.Can you see a problem the way it was done code wize?Thanks in advance.

Top
2014 / 2011 NEC & Related Books and Study Guides
#84719 - 04/28/03 08:55 AM Re: wires to panel box
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
It could be a bundling/derating issue per 310.15 (B)(2). And also, if you want to use the 2" conduit for future use, I don't believe it can be concealed. I can't remember the reference though.

Top
#84720 - 04/28/03 02:12 PM Re: wires to panel box
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
"all my circuit wiring" - is it fair to assume NM cable? (aka: Romex) - if so -
336-6(b) requires, "where passing through a floor, the cable shall be enclosed in RMC, IMC, EMT, Sch. 80 PVC, listed surface metal or nonmetallic raceway or other metal pipe extending at least 6" above the floor."

Don't see any reference regarding
'concealed' or anything about the 'abandoned pipe installation.'

Top
#84721 - 04/28/03 03:16 PM Re: wires to panel box
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
Call the inspector and ask for a code reference. If he cannot or willnot provide one, talk to his boss. The inspectors are supposed to know what they are doing, and know the code.
_________________________
ed

Top
#84722 - 04/28/03 04:32 PM Re: wires to panel box
spyder Offline
Member

Registered: 10/14/02
Posts: 211
Loc: Massachusetts
Is this a flush mount or surface mount installation?

If its flush mount then I do not see a problem with your cable installation. The bundling argument is kinda weak for residential, as there are very few continuous loads in residential. If its a loose bundle it should be okay.

If its surface mount, then his problem maybe with no protection from physical damage.

Since he has a problem with your spare conduit, I would terminate it in a proper size pull box.

Top
#84723 - 04/28/03 07:42 PM Re: wires to panel box
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
See 312.5 (C) 2002 NEC regarding the pipe.
As far as derating for bundling, I don't see that the code distinguishes between continuous or non-continuous load. If the cables are bundled in excess of 24", the inspector would have a valid point.

[This message has been edited by Redsy (edited 04-28-2003).]

Top
#84724 - 04/29/03 04:25 AM Re: wires to panel box
spyder Offline
Member

Registered: 10/14/02
Posts: 211
Loc: Massachusetts
Redsy,

My point about continuous or non-continuous loads was heat. The reason we derate conductors is to avoid a heat problem. Most conductors in residential are never fully loaded, let alone continualy loaded. Since they are not fully loaded then aren't they already derated?

If you go by the literal wording of the code, then I agree you are correct.

Top
#84725 - 04/29/03 05:40 AM Re: wires to panel box
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey Redsy that was the issue he didn`t realize the conduit was capped at the other end under home.But he sited the wiring being bundled in excess of 24 in.Ok but they are actually spread out going to the romex connectors in the panel and under the house they aren`t really bundled they are somewhat close but you know what I mean I told him I`d spread out as far as possible so he`s comming back to see.I guess there`s a gray area here up to him if he thinks they are bundled still.This is a flush mount residental.

Top