#84694 - 04/24/03 09:19 AM main disconnect
GEO Offline
Member
Registered: 03/12/03
Posts: 47
Loc: Lancaster,Pa
would a fire switch (disconnect before meter)
be wired as the main disconnect for the service? thanks GEO
Top
2017 / 2014 NEC & Related Books and Study Guides
#84695 - 04/24/03 11:13 AM Re: main disconnect
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Geo,
The only problem is that 230.91 requires that the service OCPD be a part of or be located immediately adjacent to the disconnect.
Don
_________________________
Don(resqcapt19)